  1. E

    Pre Wire for 36K Mr Cool

    Quick update.... threw a 40 amp in the breaker and system seems to be running without a problem. Ill be completing the install of the second indoor unit tomorrow, lets see if its still working well. Thanks all for your tips and recommendations.
  2. E

    Pre Wire for 36K Mr Cool

    Can I have a 40 in the breaker and only 30 on the AC cutoff?
  3. E

    Pre Wire for 36K Mr Cool

    FYI....This is a 4 zone unit. Only one zone currently installed.
  4. E

    Pre Wire for 36K Mr Cool

    Brand new install.
  5. E

    Pre Wire for 36K Mr Cool

    I have just installed and wired a new Mr Cool Mini Spit - DIY 3 ton 36K BTU (4 zone). Only 1 zone currently installed. Unit turns on and blows cold for 30+ minutes, then the fuse in the electrical panel flips and turns everything off. These are the specifications for the outdoor condenser...