I have just installed and wired a new Mr Cool Mini Spit - DIY 3 ton 36K BTU (4 zone). Only 1 zone currently installed.
Unit turns on and blows cold for 30+ minutes, then the fuse in the electrical panel flips and turns everything off.
These are the specifications for the outdoor condenser (attached): Minimum Circuit Amp 30 Amp, Max Fuse 45 Amp.
30 amp double pole breaker in the electrical box.
30 amp AC shutoff box
10/2 wire
What can I do to fix this situation?
Unit turns on and blows cold for 30+ minutes, then the fuse in the electrical panel flips and turns everything off.
These are the specifications for the outdoor condenser (attached): Minimum Circuit Amp 30 Amp, Max Fuse 45 Amp.
30 amp double pole breaker in the electrical box.
30 amp AC shutoff box
10/2 wire
What can I do to fix this situation?