  1. T

    Help wiring up a vac relay

    The Aube rc840t-120 may not be suitable for the amp draw of the motor. https://customer.honeywell.com/resources/Techlit/TechLitDocuments/69-0000s/69-2562EF.pdf I would use these knock out mounted devices. Also, did you consider useing off/on switches instead of micro switchs at each port...
  2. T

    Troubleshooting Buderus GC-124 Boiler

    The HydroStat looks like it should work, supplyhouse.com is cheaper then Amazon. https://www.supplyhouse.com/Hydrolevel-48-3200-Model-3200-Fuel-Smart-Hydrostat-Temperature-Limit-LWCO-Boiler-Reset-Control-for-Gas-Boilers
  3. T

    32+ Amp Thermostat

    1- RIBU2C relay / https://www.functionaldevices.com/products/building-automation/details/RIBU2C/ 1 - transformer 120 to 24 volt You may be able to control both heaters with a smart tstat like the Ecobee, it's a 2 stage tstat.
  4. T

    williamson boiler mod 1135-601, Temp stuck at 140F,

    Set the economy knob to minimum. The water temp should go up.
  5. T

    williamson boiler mod 1135-601, Temp stuck at 140F,

    This question is for everyone that is having this problem. What is the position of your economy adjust knob?
  6. T

    Wifi Thermostat for 60amp Heater

    Stuff :thumbup:
  7. T

    Wifi Thermostat for 60amp Heater

    For your heater I would connect the N.O. contacts of the relay to the L1 leg between the power light and the tstat. Also, set the heater tstat 5 to 10 degrees above the wall mounted tstat. Yes you can get the 115 volts from any source that's always on. The fan center mounts onto the 4x4 box...
  8. T

    Wifi Thermostat for 60amp Heater

    Yes you could use 2 relays, I would not wire it that way. But as far as using the G terminal on the tstat. It is not energized in the heating mode. It gets powered thru the Y terminal or the fan auto/on switch.
  9. T

    Wifi Thermostat for 60amp Heater

    You could wire it in place of the factory tstat. But the fan will run all the time. I prefer the fan cycle with the heat.
  10. T

    Wifi Thermostat for 60amp Heater

    Here you go Auto Tech.
  11. T

    Wifi Thermostat for 60amp Heater

    Yes you could use a dial or digital tstat. The OP wants to connect a smart tstat to have the ability to operate the heater from inside of his house. The transformer for the setup I described is for the control circuit. Its 115 volt primary to a 24 volt secondary. It will power the relay and...
  12. T

    Williams Forsaire Counterflow...Correct behavior?

    Whats the model and serial #?
  13. T

    Wifi Thermostat for 60amp Heater

    The way I would go about installing a remote tstat for this heater is as follows. 1-Get a fan control center that will handle the amp draw for the fan and a 4x4 electrical box. 2-Run a 115 volts to the 4x4 box to power the transformer. 3-Run 2 wires from the 4x4 box to the heater. Connect the...
  14. T

    Goodman GMPN 080-4 natural gas furnace

    How long has the been happening? Also, has the gas valve been replaced?
  15. T

    Trane ceiling hung forced hot air unit

    NP your welcome!
  16. T

    Trane ceiling hung forced hot air unit

    Can you post a picture of the name plate and of the unit?
  17. T

    Trane ceiling hung forced hot air unit

    The NO/NC switch is a safety limit. It will turn off the gas valve if the heat exchanger got to hot due to the fan not working. The time delay relay allows the heat exchanger to heat up before the fan starts. It should also allow the fan to run after the gas valve closes to cool the heat...
  18. T

    Furnace duct fittings?

    Try to find an HVAC company that could make it for you.
  19. T

    Furnace duct fittings?

    Its called a plenum. I would look for a prefab one or get one made to fit the furnace. Then put a round collar on the top to connect to the round ductwork.
  20. T

    test

    Testing of avatar.