I had an almost catastrophe this morning in the shop with my G73 heater, and I wanted to see if anyone else has seen this.
Yesterday, I could smell electrical smell yesterday, but couldn't pin point it (I have a 1200' shop, lots of choices.) I figured it was just some dust on the battery charger or something, so I didn't really try very hard. I should have.
I came out this morning to a cold shop (it's been 20 and 30 below here), and noticed a big (9-10" black streak behind the thermostat.)
I opened it up and it was all melted to hell. The wires inside had totally melted.
That could have been bad, and about $150k worth of cars, parts, and shop. I'm insured, but what a mess.
I opened up the King brand t-stat, and indeed, it's rated to 22A, and I'm using 10g wire as I should have. The wire from the heater to the tstat is only about 7' long.
Is it just possible that it was a defective unit? Since it's been so cold, the heater has been cycling a LOT, so perhaps a defect in combination with extra cycles just heated up the wiring?
I don't suppose there's any way to prevent that, right? I mean, the breaker didn't trip because there was technically no fault on the power side (the one going back to the breaker.)
I don't have (nor do I need) an on/off switch on the wall. In the summer, I just flip the breaker, and the rest of the year (like 7 months), I just use the tstat.
We travel a bit, and the shop is left unattended for a month at a time, in the winter, and I'd hate to see this happen again, or worse, bring the whole shop down.
Any advice for moving forward? I ordered a new T-stat, higher amperage this time, like 25A.