mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
nope but some gfcis have guidelines as to length of wire on the load side. also realize that the more stuff you have downstream the more you effectively lower the trip threshold. Good design practice is to limit wire length on the load side of GFCI.
 

v8garage

Well-known member
Joined
Jun 27, 2007
Messages
901
Location
Texas
When you buy a good quality GFCI the paperwork that comes with it will tell how many outlets it will handle.
V/8
 

rockchucker

Well-known member
Joined
Mar 27, 2010
Messages
1,764
Location
Seattle WA
Sounds like it comes down to the Circuit.


Here...


For a dwelling unit, let your conscience be your guide as to the number of general purpose receptacle outlets on a branch circuit because there is no NEC limit, but since this sounds like it is a non-dwelling application, 220.14, Branch-Circuit Load Calculations applies for branch circuit receptacle outlet loading, not merely for service and feeder calcs.
Using 220.14, a maximum of 13 receptacle outlets are allowed on a 20A circuit. They can be single or dulpex and still only counts as one receptacle.
The exception would be for simultaneous and non-simultaneous use of receptacles on multi-outlet assemblies [Plugmold] and single piece of equipment with four or more receptacles.
You don’t need to allow for 80% max load on a branch circuit used for these receptacles, the 80% limit is on the receptacle itself. 16A max load on a 20A receptacle, see Table 210.21,B[2]. The 125% [80% max] branch circuit rating your thinking of applies to equipment on individual branch circuits.



Next time you open a GFCI box, look to see how many "protected BY" stickers are in there. P & S has 7 stickers. They put the quantity in there for a reason, 1 gfci receptacle and 7 non-gfci receptacles stickers...adding up to 8 receptacles on a gfci.
 
OP
M

mrobins297aaa

Well-known member
Joined
Sep 20, 2010
Messages
3,283
Location
south east michigan
I'm wiring my pole barn
it seems like the last time I wired some gfcis it did say in the instructions how many could be on the load side, but these's cheapeze that I bought don't say anything.
I'll have to check how many stickers are in there.
thanks for the info
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I have used between 4 and 6 general purpose outlets south of low cost GFCIs and not had any trip problems, even with a 3/4 HP drill press on the circuit, bench grinder, 110V welder, etc.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
You can put a pigtail to feed the GFCI outlet.Then continue your outlets with out GFCI protection if you wish.Hope this helps!

Not in a garage - all must be GFCI unless dedicated to some operation like a drill press. Least that's what I've picked up. Code requires GFCI outlets in a garage.
 

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
I went with all 20a receptacles, and 20a GFCI's, on 12Ga Romex, and kept it to four or less receptacles beyond each GFCI. Overkill? Maybe.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
If you are buying 20 amp receptacles (non-GFCI) thinking they are better, think again. The internals of a Leviton 15 amp Pro Grade and a 20 amp Pro Grade of the same type/part number series, is identical. The only difference being the face plate attached to the receptacle during manufacture, and the price in the store.

Charles
 
To avoid these ads, REGISTER NOW!

Teken

Well-known member
Joined
Jan 2, 2010
Messages
8,214
Location
The Bad Lands
If you are buying 20 amp receptacles (non-GFCI) thinking they are better, think again. The internals of a Leviton 15 amp Pro Grade and a 20 amp Pro Grade of the same type/part number series, is identical. The only difference being the face plate attached to the receptacle during manufacture, and the price in the store.

Charles

This is so true . . . I found this out the hard way many years ago. Now, having said that residential, industrial, and hospital grade outlets are indeed made different.

The tolerances and spec's for a hospital grade outlet is a lot more than a standard residential Home Depot outlet.
 

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
If you are buying 20 amp receptacles (non-GFCI) thinking they are better, think again. The internals of a Leviton 15 amp Pro Grade and a 20 amp Pro Grade of the same type/part number series, is identical. The only difference being the face plate attached to the receptacle during manufacture, and the price in the store.

Charles

Oh, and then there is the fact that it is rated and stamped as "20-Amp", and has a 20 Amp blade configuration, which makes it 20-Amp rated, unlike the "identical" 15 Amp unit.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
unless its a single receptacle (not a duplex) on a 20a circuit there is no reason to use 20a receptacles unless you have stuff with 20a plugs on it.
 

FlyNFuzz

New member
Joined
Oct 28, 2013
Messages
1
GFCI Problem

:eyecrazy:

I have a fairly new 15 amp GFCI in a kitchen counter outlet. The load side has 3 additional 15 amp outlets. These are located within about 15 feet of run, in the next room.

The GFCI outlet and the next outlet in the run work fine. But whenever any item is plugged into outlet 2 or outlet 3, the GFCI immediately trips.

Using a standard GFCI tester, GFCI outlet and the next outlet in the run test out correctly. And when the fault button is pressed, the GFCI outlet and the next outlet in the run trip the GFCI - as they should.

Outlets 2 and 3 in the run - the ones that immediately trip the GFCI whenever any load is plugged in - also indicate that they're correctly wired. However, when the fault button is pressed on the GFCI tester when its plugged into either outlet 2 or outlet 3, the GFCI will not trip

So I'm a bit stumped. How can the tester indicate correct wiring while the fault button won't trip the GFCI on either of these two outlets, but anything else plugged into either outlet immediately trips the GFCI ?
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Re: GFCI Problem

:eyecrazy:

I have a fairly new 15 amp GFCI in a kitchen counter outlet. The load side has 3 additional 15 amp outlets. These are located within about 15 feet of run, in the next room.

The GFCI outlet and the next outlet in the run work fine. But whenever any item is plugged into outlet 2 or outlet 3, the GFCI immediately trips.

Using a standard GFCI tester, GFCI outlet and the next outlet in the run test out correctly. And when the fault button is pressed, the GFCI outlet and the next outlet in the run trip the GFCI - as they should.

Outlets 2 and 3 in the run - the ones that immediately trip the GFCI whenever any load is plugged in - also indicate that they're correctly wired. However, when the fault button is pressed on the GFCI tester when its plugged into either outlet 2 or outlet 3, the GFCI will not trip

So I'm a bit stumped. How can the tester indicate correct wiring while the fault button won't trip the GFCI on either of these two outlets, but anything else plugged into either outlet immediately trips the GFCI ?

Do outlets 2 and 3 work when the GFCI is tripped? If you haven't checked, do so, it may be that they are wired to the line side rather than the load side of the GFCI and are not protected by it.

If you didn't wire it, there is no telling what some flunky electricians helper did.

Charles
 

Kevin C

Well-known member
Joined
Aug 4, 2011
Messages
1,653
Location
Portland OR
Re: GFCI Problem

Do outlets 2 and 3 work when the GFCI is tripped? If you haven't checked, do so, it may be that they are wired to the line side rather than the load side of the GFCI and are not protected by it.

If you didn't wire it, there is no telling what some flunky electricians helper did.

Charles

My guess is that the neutral and the ground are connected or swapped down stream of the GFI.

Or the neutral for the down stream outlets is coming off of the wrong terminal on the GFIC.

Or... The down stream outlets are connected to the wrong neutral ( from another circuit).
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,004
Location
Modesto, CA
If you are buying 20 amp receptacles (non-GFCI) thinking they are better, think again. The internals of a Leviton 15 amp Pro Grade and a 20 amp Pro Grade of the same type/part number series, is identical. The only difference being the face plate attached to the receptacle during manufacture, and the price in the store.

Charles

I bet youre getting sick of repeating this over and over again just like I'm getting tired of explaining the difference between a GROUND rod and a GROUND wire(EGC) and why u cant connect an outlet EGC to a ground rod and say the outlet is properly grounded....uggg :lol_hitti
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
I bet youre getting sick of repeating this over and over again just like I'm getting tired of explaining the difference between a GROUND rod and a GROUND wire(EGC) and why u cant connect an outlet EGC to a ground rod and say the outlet is properly grounded....uggg :lol_hitti

This is an old thread, brought back from the dead, but you are correct, I have said it a few times before and a bunch since.

Several people on here argue that there is no difference in price between the 15 and 20 amp but if you go into a big box store, there is, and if you look online, there is, and so, for the most part there is a price difference, even if the supply houses don't charge any different to a contractor on a bulk amount of them. To me, any amount more it too much, as I've never encountered a 20 amp/120v plug installed on a device or piece of equipment.

What!!! you mean that I gotta go change the ground wire I connected to my PVC water pipe/air plumbing :beer:

Charles
 

Zrxpilot

Well-known member
Joined
Nov 19, 2011
Messages
62
^ I recently purchased a few Leviton industrial grade 20 amp outlets for my shop. Found them ebay for like 5 bucks a pop. Perhaps they are all that way but these 20amp outlets had very nice push-thru wire clamps that fit 12g wire. Clamped up nice and tight

Not that many outlets in my shop. Probably spent an extra 20 bucks for some piece of mind.
 