So there a several (very several) threads about water condensation, and the Franzinator in particular. There has not been, to my knowledge, any thorough analysis of what actually needs to happen to make dry air come out of a hose, or what the end-all, be-all best way to do it is. So, I'll show my cards, and submit what I've discovered while trying to reduce this down to a math problem. If I have made any errors, please help me out and see where this discussion goes.
Dew point. Dew point is defined as the temperature below which the water vapor in a volume of humid air at a given constant barometric pressure will condense into liquid water at the same rate at which it evaporates. Thus, to remove as much water as possible from the air, we want the Dew point to be as high as possible. Dew point is a function of Relative Humidity. If we can get the RH to be 100%, then we have achieved the goal of maximum Dew point, and therefore maximum condensation.
RH is defined as the ratio of the partial pressure of water vapor in the air, to the evaporation pressure of any liquid water in the same volume. This means we want the partial pressure to be as high as possible, and the evaporation pressure to be as low as possible.
HERE'S MY ASSESSMENT- maximizing partial vapor pressure is a function of the air pressure itself, which means it's dictated by the regulator on the tank. If your reg is set to 150, and you don't have any significant restrictions along the way, then your partial vapor pressure is fixed, and is not affected by the air temp. Raising the regulator setting will increase water removal.
Evaporation pressure of the liquid, however, is not affected by pressure but IS affected by the temperature of the water. Making this temperature lower will increase water removal. Note that without using any refrigeration equipment, the lowest possible temperature is going to be whatever your ambient temp is. Therefore, if you don't want a refrigerated system, all you need to do is reach ambient at max PSI, and then separate the water. If you leave the water in the tank, and start running your tools, the drop in pressure will cause the liquid to re-evaporate.
So in essence, if you can get the compressed air to return to ambient temp before hitting your tank, you will have the driest air possible for your situation.
So what about the Franzinator? Franz says that the pressure drop causes a temperature drop (which is true) and that the temperature drop causes further condensation (which I am about to disprove).
Remember the RH? Dropping the pressure of the air does drop the temperature- OF THE AIR. Notice how the partial vapor pressure was not affected by the air temp? It's only dependent upon the pressure, which we just killed by using a restriction/expansion chamber. Thus, our RH has dropped, and along with it, the Dew point. The "refrigeration effect" does not exist. Further to illustrate the point- the low pressure area of a refrigeration system is called and "evaporator", not a condenser. Refrigerant evaporates when it is expanded- why would water be any different?
What the Franzinator DOES- is give a large, heavy chunk of metal for the air to contact, which acts as a heat-sink to drop the air temp back to ambient faster than it would otherwise. It's adding cooling capacity. It also acts as an air separator. If your setup already brings the air back to ambient before hitting the hose, and gives the liquid someplace to go without being caught in the airstream, you're good to go and don't need this thing.
TL;DR: Nothing special about the Franzinator that any other method of adding metal to the distribution line wouldn't also accomplish.
You must run the outlet of the compressor head to the center of the "Franzinator".From there into the tank and then from tank to air piping.Please correct me if I am not seeing your pictures correctly.You will see a huge change in how it works if you swap it around and you will keep most of the moisture out of the tank.