I really do have quite the mall to go comparison shopping right at work. I work at Honda Aircraft and we have many large and small bays to get ideas from.
But for example we have a wood shop about the size of my garage with only 8 4' fixtures not sure if they are T8 or T12 but the lighting in that shop is adequate for that shop.
Fair enough; but those aren't the only variables. Among the other things we (or more importantly, you) would need to make an even semi-valid comparison would be:
-- The number of tubes in each fixture
-- The specific TYPE of tubes. There can be a whale of a difference in output between various different "four foot" tubes.
-- The height of the ceiling in that shop
-- The height at which the fixtures are mounted
-- The specific photometrics of those particular fixtures, especially if they are even vaguely similar to "High Bay" types.
-- The way the ceiling, walls, and floor are finished
But I realize that if I had a car in there working on the side against a wall the light would be blocked and it would be inadequate. So overall lighting I would say is good and in fact appears to be even, but the ability for that setup to not be blocked by large object like cars would really ****. That is why I like the 3 row strip lighting for the garage. It will essentially hit everywhere.
And that is exactly why I also often recommend what I call the "Big 'U'" or "Big 'W'" layouts.
I think what I will do is get the dimensions of that shop and light models and model it in the Acuity software. That would be a good baseline starting point.
That could be interesting,
IF you can get ahold of all of the pertinent data with sufficient accuracy.
Wow quite a post. I best not re-quote and I certainly appreciate you taking the time.
You're welcome. And please don't let the little "Tempest in a Teapot" between Joe and myself throw you off-track.
My understanding is that you are concerned with shadowy areas which I understand but at 92 cf overall with some lights turned off those shadowy areas would be in the neighborhood of 46 cf which is considered acceptable for general auto repair according to manufactures guide lines.
Ahhh, HA!
I think we may have just discovered the root source of some of your misunderstanding, and in turn why you have been
SO recalcitrant about installing really adequate lighting...
In short: It doesn't work that way.
Even in the most perfectly idealized lighting plan, that "average brightness" figure is just that: a statistical AVERAGE. There WILL be some areas which are brighter than others, and in turn, some which are dimmer. And MOST importantly, just saying that a given plan produces "NNN lumens/ft.^2" does NOT address this in any way! For purposes of illustration, let's just throw an arbitrary dart and say that for some imaginary "decent, but not perfect" lighting plan, this bright/dim variance is perhaps 20% of the overall average. So if the "average" illumination of the entire space is 100 lumens/ft.^2, you could expect some areas to be about 120 lumens/ft.^2 and others to be about 80 lumens/ft.^2. (FWIW, minimizing this difference is part and parcel of creating a GOOD lighting plan.)
Now, a very critical point: If/when you arbitrarily disable ANY of the individual light sources within that plan, you necessarily make the difference between the "bright" areas and the "dim" areas MUCH more extreme.
So, let's take your example above... If the overall average illumination level is 93 lumens/ft.^2 with all the lights on, turning off half of them would indeed make the new "average" 46(.5) lumens/ft.^2. But again, that's the OVERALL AVERAGE for the entire space. Furthermore, it should be intuitively obvious that the "bright" areas did NOT get any brighter. So it follows that the "dim" areas necessarily got
MUCH dimmer -- in fact, they probably fell to near-zero, if that 46(.5) lumens/ft.^2 overall "average" is to be maintained. [In practice, it would not be QUITE that bad, due to "spillover" from one area to the next. Also, by turning off some fixtures, we are also killing some of the (formerly) "bright" areas in the process, which also works to lower the overall average without requiring the "dim" areas to actually go to zero. But regardless, the fundamental point -- which I'm probably not explaining very well -- remains.] This is why we want the maximum "granularity" possible when implementing such a "two-stage" lighting system, so that the "dim" areas we create when dousing SOME of the lights are kept as small as possible, and thus the "spillover" from the adjacent fixtures has a smaller "hole" to fill.
At the same time this is a 1 maybe 2 person shop. If I'm working on the left side of the car I turn on the left lights ect.
True; but this gets us back into "zoning" vs. "intensity control". And really, if you're doing a brake job, or the twice-yearly Summer/Winter wheel & tire change-over, or simply detailing the car... Do you REALLY want to have to re-adjust your lighting in the middle of the job?
My main concern is that the light hits everywhere which I have found to be more important than how bright it is. The three row solution addresses that even when some of them are off.
As alluded to above, and notwithstanding any nitpicks about what exactly those "rows" should consist of, I largely agree with you on this, at least in principle. I've said here many times that proper location of the light sources is AT LEAST as important as (and usually more important than) the total light level, as long as the latter is not allowed to go way off-scale. Your "three row" approach is essentially the same thing as my "Big 'U'" or "Big 'W'" approach, save for my ALSO using a fourth "crossways" row near the front of the vehicles (i.e., a few feet off the back wall). This addition does two things, both important: It lights up whatever cabinetry, shelving, or other storage which may be mounted to that back wall; and it throws some additional light into the open engine compartments of any parked vehicles.
Of course your solution is optimum in customizing ability but there are the things I have to consider as well. One being cost ~ 75% more, the other being lack of simplicity as in 21 ballast to maintain verses 9 and then installation. I will have to weigh these up.
I'm not sure I'm following you here. There's no way on this planet that simply going to 4-foot fixtures in place of tandem 8-footers would add 75% to the cost. In fact, depending on the specific fixtures in question, it MIGHT even be cheaper (tho' that's a hair I'd prefer to not split -- it is rarely productive to try all that hard for
THE cheapest solution).
As far as adding an additional 4 footer to take up the last two feet at each end I believe that wont be feasible due to roll up door hoods that would be physically in the way of the installation with the exception of the center strip.
If I understand what you mean by "door hoods" correctly, that should be a non-issue. With roll-up doors, placement of those "outer" runs is somewhat less critical than it would be with conventional overhead doors; but presuming you have the room (which I think you do), they probably still ought to be mounted outside the "footprint" of the doors themselves. And like I said before, if seven four-footers is too tight a fit, then six four-footers and one two-footer will solve the problem.
As far as the light scene switch, are you saying it has the capability of physically dimming lights, or just turning some on and some off.
Depends on the specific keypad/switch/load-module chosen. That in turn depends on the type of load they will need to control. The ones I pointed you to are designed to be used with fluorescent lights (which are themselves inherently non-dimmable); and so they use relays to switch the load, and do not offer a dimming capability. Hence, your "intensity control" is accomplished by running more/less fixtures at any given moment.
And can it be made to work with 2 circuits.
Do you mean two breaker circuits? Sure. Each given "bank" of lights would be controlled by a single load module (be that a keypad, a paddle switch, or an in-line module). You WILL have at least three of them en toto (one for the "walk through" lights, and two for the "main" lighting), just as would be the case with conventional switching. In turn, you power these various load modules from one breaker or the other, making sure that at least the two "main" banks are on different breakers -- again, just as with conventional switching.
In any case the scheme for now remains at 9 8 footers at 92 cf. Spacing will be modified to place the side rows 3ft from the walls and cross lighting up front can be evaluated and installed as required.
PLEASE heed what I said above, and use the four-foot fixtures! The ONLY down side is a bit more complication in the wiring and installation; and that is a trivial concern in the long run.
Machine shop will be a different animal because generally I work all over the place. So a even distribution of light is required. I probably will do the garage first to evaluate and then decide how to do the machine shop.
For the machine shop, a more-or-less conventional "rank & file" arrangement will likely be your best bet.
I do not believe that any reasonable system will negate the use of task lights at machines be them flash lights or a halogen machine light aiming at the tool action.
I tend to agree.