1/2 copper tubing not big enough?

catch22

Well-known member
Joined
Apr 13, 2008
Messages
95
I had a guy tell me that my gas line from my house to the garage is to small,it is 1/2 od 3/8 id copper tubing and is about 45 feet long then it goes into 1/2" black pipe. I will be running a 45000 btu natural gas overhead heater,my question is will the 1/2" copper be big enough and if not what will happen if I try to use it anyway?


Thanks Mike
 
To avoid these ads, REGISTER NOW!

A_Pmech

Well-known member
Joined
May 8, 2007
Messages
8,002
Location
IL
Is this a single-stage or two-stage system?

If you run a two-stage system, that 1/2" line will support a LOT more than 45,000 BTU.

For information on sizing, download Rego's "LP Gas Serviceman's Manual" from their website.
 
OP
C

catch22

Well-known member
Joined
Apr 13, 2008
Messages
95
I havent bought the heater yet,what is the difference between single stage and 2 stage systems?
 

redsky49

Well-known member
Joined
Jan 21, 2009
Messages
582
Location
near the coast in eastern North Carolina
The pipe should be sized based on the maximum potential demand. Doesn't matter if multi-stage or single stage burner.

1/2" copper is at the limit of typical system pressure drop (0.3" pressure drop per 100') for low pressure gas service.

I would recommend 3/4" if starting from scratch, or look for a smaller heater.

As always, offered only as opinion

Edit:
If you have a 2 psi gas service, you will have more than enough supply. If you are dealing with a typical residential gas system of 5-7" pressure, the 1/2" pipe is too small.
 
Last edited:
To avoid these ads, REGISTER NOW!

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,955
Location
Southern Indiana
The pipe should be sized based on the maximum potential demand. Doesn't matter if multi-stage or single stage burner.

1/2" copper is at the limit of typical system pressure drop (0.3" pressure drop per 100') for low pressure gas service.

I would recommend 3/4" if starting from scratch, or look for a smaller heater.

As always, offered only as opinion

Edit:
If you have a 2 psi gas service, you will have more than enough supply. If you are dealing with a typical residential gas system of 5-7" pressure, the 1/2" pipe is too small.

Rant=ON

As someone who works for a gas company, let me just tell you how much I "Love" customers who are so cheap or shortsighted that they didn't run big enough pipe and want me to come in and redo their meterset for a 2PSI system. It may not seem like a big deal, but just the correcting meter index alone costs about $50 and I have to replace the regulator too, with something like a sensus HP 143...which likely costs another $50. Meanwhile...the customer is suddenly taking eight times as much gauge pressure into their home where they are going to need regulators to handle that pressure, because the appliances need to see 7 inches w/c or so. That's more expense on their side that likely eats any savings they achieved by staying with the smaller pipe, and if they get a LEAK on their piping it will leak more than it would have at a lower pressure.

Meanwhile, our meter set is no longer standard, meaning if there is a problem someday, there is almost a 100% probablility that the serviceperson responding will NOT have the correct parts on his truck to fix the problem.

If someone can save 50-cents they want to save it, even if it costs us $100 to save them that 50-cents.

For God's sake people. Just run adequate sized piping.

Rant = off.

Phil
 
Last edited:

A_Pmech

Well-known member
Joined
May 8, 2007
Messages
8,002
Location
IL
I had a guy tell me that my gas line from my house to the garage is to small,it is 1/2 od 3/8 id copper tubing and is about 45 feet long then it goes into 1/2" black pipe. I will be running a 45000 btu natural gas overhead heater,my question is will the 1/2" copper be big enough and if not what will happen if I try to use it anyway?


Thanks Mike

Mike,

My mistake...

I mis-read your post and thought you had an LP gas system instead of a Natural gas system.

Here's some info on sizing the low pressure side of a Natural gas system that may be of help:

http://www.engineeringtoolbox.com/natural-gas-pipe-sizing-d_826.html

Sorry for the confusion.
 

redsky49

Well-known member
Joined
Jan 21, 2009
Messages
582
Location
near the coast in eastern North Carolina
I would never recommend a 2psi system for a residential system, though on occasion I have seen it done when there were no other alternatives. Commercial and institutional applications are another matter. In any case, I would not bring the higher pressure into the structure. Provide the regulator outside of the garage if you decide to go this route.

Most likely the original poster has only 7" supply. In this case, leave the existing buried 1/2" copper for a future water supply to the garage, and provide a new 3/4" for your gas supply.

Be careful with gas, whether propane or natural gas.

As always, offered only as opinion
 