10-2 for light duty 220

Kev442

Well-known member
Joined
Jan 15, 2009
Messages
5,386
Location
Wi
I was wondering if you would go for it. I want to run 125' of 220 and 110 wiring to the out building. A spool of 10-2 250' is ideal, 1/2 for each run. Now I have used 10-2 for short temporary 220 runs in the past, so I know it will do it, but would you run it permanently to run a 20 amp air compressor? The price difference to buy 10-3 250' is substantial.
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
You can't legally run more than one branch circuit/feeder to a building. Your 10-3 is OK, but two 10-2's are not.
 
OP
K

Kev442

Well-known member
Joined
Jan 15, 2009
Messages
5,386
Location
Wi
I hadn't even considered that two wires is not legal. Seems silly (and more dangerous) to run one wire fully loaded and then have to split the circuit as opposed to two wires getting much lighter duty. Offhand, I would say there are a lot of illegally wires outbuildings around here.
Anyway, I'll put that down as a no on 10-2 from you.
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Seems silly (and more dangerous) to run one wire fully loaded and then have to split the circuit as opposed to two wires getting much lighter duty.

It's not silly and more dangerous running a single cable out there if you size it properly. You stated 20 amp air compressor, which means absolutely nothing without knowing the voltage. If it's 120 volt that still frees up one leg of that 10-3 cable. If it's 240 volt, your going to want a larger cable than 10-3.

And yes, they're are a lot of illegally wired outbuildings out there. I can't count how many I've seen fed with direct buried Romex.
 
Joined
Apr 4, 2005
Messages
11
Location
Lansing, Michigan
You can't legally run more than one branch circuit/feeder to a building. Your 10-3 is OK, but two 10-2's are not.

You sure about that? I had a licensed electrician run two branch circuits to my outbuilding and he never said anything about it being an issue. I've got 12-2 and 10-3, both UF cables direct buried in a trench that goes below the frost line.

There's also 2" Schedule 80 conduit in the same trench, with a flexible compressed air line inside the conduit. As far as I'm aware, none of that is illegal or against code.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
as far as two cables, the reason this is a no no is all of a circuit's conductors have to be in the same cable or raceway.

To the guy with two circuits: so the guy that did it was licensed....did he pull a permit and have it inspected? Two circuits (a MWBC counts as one) to a detached structure is illegal. There are a couple exceptions. For example if you have a light in the outbuilding controlled by a switch in the house, that can have its own cable.
 