All, I need to wire up two pool pumps. I have 10-3 NM in crawlspace, what is the legal way to pass through the brick?

I need to pass through the brick then up for about 4ft and terminate into a small sub panel.

Do I need a junction box in crawlspace transitioning NM to THHN/THWN or can I legally run the NM in the conduit up to the sub panel then transition to the proper wire there?

I've read a number of threads this subject, seems sort of subjective, but I wanted a get a sanity check anyways.
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,606
Location
Long Island
The panel feeding a pool pump needs a full sized insulated ground. I do not believe you can feed it with NM.
 
OP
K

K Powers

Well-known member
Joined
Jul 17, 2013
Messages
105
Location
Alabama
The panel feeding a pool pump needs a full sized insulated ground. I do not believe you can feed it with NM.

OK interesting Ill look into the ground subject

And just to clarify its an exterior wall of the home not detached.
 

wedangpanas

New member
Joined
Jul 21, 2016
Messages
4
OK interesting Ill look into the ground subject
g.png

And just to clarify its an exterior wall of the home not detached.

Good luck K power,Its same with my issue
 
To avoid these ads, REGISTER NOW!

marklc

Well-known member
Joined
Nov 24, 2015
Messages
82
May be able to use UF also (underground feeder) depending on your local codes.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
There are only 2 locations recognized by the NEC, dry and wet.
Any exterior location is considered to be a wet location.

The ground should be individually insulated, just the same as for an active conductor. The jacket on UF cable doesn't qualify.
 

shillamus

Well-known member
Joined
Sep 6, 2015
Messages
75
There are only 2 locations recognized by the NEC, dry and wet.
Any exterior location is considered to be a wet location.

The ground should be individually insulated, just the same as for an active conductor. The jacket on UF cable doesn't qualify.


So even inside of liquid tight conduit is considered exterior???
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Probably so, I think maybe they allow the G in UF to be considered insulated? But if this was a pipe out of the direct weather and under overhang where it cant get flooded it wouldn't cause me any loss of sleep.
Someone can elaborate but the idea is an insulated ground so it cant become energized from any other source and is not shared with other circuits. Its been a while since I read thru the section, as Alfred pointed out very specific rules concerning pool feeds.
I usually don't say much at Home Depot but the other day the plumma and a customer were discussing hot tub hook up, this was a first diy job for the guy, neither knew if the thing was 120 or 240, yikes.
 