My shop is relatively new, all pre wired and finished. Now that I have an increased requirement for air, my dedicated compressor circuit should have been 8 ga. min. I'm stuck with the approximately 60' run of #10 and the 5 hp, 60 gallon , 2-stage isn't going to happen. I can surely get by with less but was hoping for low rpm quiet quality. With cost not being an issue, what is the next best thing? build it? order it? existing unit?
 
To avoid these ads, REGISTER NOW!

kkroger

Well-known member
Joined
Apr 21, 2013
Messages
1,143
I've got a 7 hp Single Stage Running on 10 AWG here at my house with an 80' Run and no issues, Have a 5 HP IR Two Stage Running on a 100' 10 AWG run at the shop with no issues...
 

laajmalek

Member
Joined
May 27, 2017
Messages
6
What seems to be the problem? I'm not really sure if you stated a direct problem you are having other than you have 60' of 10 AWG instead of 8 AWG wiring.

That 5 HP motor and pump should be fine on 60' of 10 AWG.

Sent from my XT1254 using Tapatalk
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
5hp motors supposed to be 28 amps and you need 125% so 35 amps. You may not find 35 breaker so it needs to be 40 and 8 gauge wire. That's if it's a TRUE 5hp

But. If you go to big box store and look at their motors. For example My 80 only says 22 amps on the nameplate and you get a 5hp sticker on the compressor. Nowhere on the nameplate says HP is 5! If I go by this number of 22 amps at 125%. Only requires 30 amp breaker and 10 ga wire. In fact the manual in mine tells me to use 30 amp. For insurance purpose if something happens they would look at what the manufacturer says and cannot fault me for having 10 ga wire.

I would go in this order unless someone thinks otherwise.
Manufacturer recommendation of breaker
Then. Name plate to determine breaker
Then NEC generic description of what 5hp should be. (28 amps before safety factor)


That said there are 80g compressors that is in the 20 cfm range. I don't think they would run on a 30 amp circuit since they would be closer to a True 5hp motor
 
To avoid these ads, REGISTER NOW!

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,893
Location
oregon
My shop is relatively new, all pre wired and finished. Now that I have an increased requirement for air, my dedicated compressor circuit should have been 8 ga. min. I'm stuck with the approximately 60' run of #10 and the 5 hp, 60 gallon , 2-stage isn't going to happen. I can surely get by with less but was hoping for low rpm quiet quality. With cost not being an issue, what is the next best thing? build it? order it? existing unit?

This issue has been discussed a few times on this forum and the real electricians, not me, have cited chapter and verse of the goodbook where you can over-breaker a wire on a compressor circuit. 10 ga should work for a true 5 hp motor. No need to go outside of the norm for a compressor.

lg
no neat sig line
 

md21722

Well-known member
Joined
Nov 30, 2015
Messages
1,840
Location
Mt Juliet, TN
#10 and 5HP is permitted by code if the wire is THHN in conduit. If it's NM-b (Romex) then #8 is required by code.

Why not run a new line and use your existing line for a welder?

Both Champion and Jenny do sell 3HP dual stage air compressors.
 

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
5hp motors supposed to be 28 amps and you need 125% so 35 amps. You may not find 35 breaker so it needs to be 40 and 8 gauge wire. That's if it's a TRUE 5hp

But. If you go to big box store and look at their motors. For example My 80 only says 22 amps on the nameplate and you get a 5hp sticker on the compressor. Nowhere on the nameplate says HP is 5! If I go by this number of 22 amps at 125%. Only requires 30 amp breaker and 10 ga wire. In fact the manual in mine tells me to use 30 amp. For insurance purpose if something happens they would look at what the manufacturer says and cannot fault me for having 10 ga wire.

I would go in this order unless someone thinks otherwise.
Manufacturer recommendation of breaker
Then. Name plate to determine breaker
Then NEC generic description of what 5hp should be. (28 amps before safety factor)


That said there are 80g compressors that is in the 20 cfm range. I don't think they would run on a 30 amp circuit since they would be closer to a True 5hp motor
If you look at those big box store "5 hp" compressors the motor invariably says "Special " or anything but 5hp. on the plate. I guess the pump is a 5hp capable. You see that in LED flashlights that say "3 watt Cree bulb" but are not running anywhere near 3 watts.

Sent from my SM-G900V using Tapatalk
 
OP
M

Majordisorder

Well-known member
Joined
Jan 5, 2014
Messages
234
Location
North Idaho
#10 and 5HP is permitted by code if the wire is THHN in conduit. If it's NM-b (Romex) then #8 is required by code.

Why not run a new line and use your existing line for a welder?

Both Champion and Jenny do sell 3HP dual stage air compressors.

This is what my research came up with and my wire is 10-2 romex. My welders are already taken care of so will check out the Champion and Jenny. Thanks.
 