Hello Everyone,

I just added the 10" Sioux grinder to my collection. It's a 1 HP motor that can run on 220 or 110. I have three other Sioux grinders, but smaller Hp., that run on 110. What are the advantages and negatives to run this one on 220?

Thanks,

Ron
 
To avoid these ads, REGISTER NOW!

Mohawk Dave

Well-known member
Joined
Oct 7, 2012
Messages
5,068
Location
SoCal
Less wear and tear to the motor (less heat generated)(and I think we're splitting hairs at this point)...even though a good Sioux would last forever on 110 when cared for.

I'm curious to see what the experts have to say....

BTW, I just redid my Duralast 10" 2hp 110/220v 18.5amp this weekend. I'm running it on 110...just b/c I move it around.
 

Attachments

  • DSCN9618.JPG
    DSCN9618.JPG
    119.8 KB · Views: 31
  • DSCN9619.JPG
    DSCN9619.JPG
    113.3 KB · Views: 30
  • DSCN9620.jpg
    DSCN9620.jpg
    139.4 KB · Views: 26
Last edited:

zkling

Well-known member
Joined
Jan 23, 2007
Messages
16,939
If both circuits are properly set up (sized) for the application there will be no running difference in the grinder. The problems start to arise and differences become noticeable when someone changes a 110v saw on a 15amp breaker in a 50' extension cord, to a more equipped (read proper) , 8' run 220v outlet.
 

bobcatdan

Well-known member
Joined
Jan 4, 2011
Messages
9,948
Location
Kaukauna,WI
If you have a spare 220 outlet just sitting wide open in the exact spot you want to put the grinder then run 220. If you have to do any wiring at all, it is not worth the work and run it 110.
 
OP
S

scrapdaddy

Well-known member
Joined
Dec 5, 2011
Messages
126
Location
Dittmer, Mo.
So, you guys are saying it wouldn't run any better on 220, more rpms, won't bog down, etc. I've got 220 in the shop, but would have to special wire to a spot for the grinder. No reason for it, if not worth the trouble.

Any of you guys collect the Sioux grinders. I've got four different models, so far.

Thanks for the responses.
 
To avoid these ads, REGISTER NOW!

Davefr

Well-known member
Joined
Jan 7, 2010
Messages
11,842
Location
OR
It will run better on 220VAC!! Since less current is required, the resistive power loss that occurs in the motor and the circuit will be less. (simple ohms law: P=I squared X R). Less power loss = less voltage drop.

The difference is not usually dramatic, but given a choice always opt for the higher voltage option.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,152
Location
Minneapolis
For a 1hp motor it won't make enough difference to matter either way. However, it will need a 20 amp circuit, so if you only have 15 amp 120vac circuits in your garage you'll want to go with a 240vac connection.
 
OP
S

scrapdaddy

Well-known member
Joined
Dec 5, 2011
Messages
126
Location
Dittmer, Mo.
Thanks guys, good information. I have 20 amp circuit breakers in the shop and 50 amp & 30 amp for the welders and air compressor. So, leave it at 110.