Ok I have been doing a lot of reading here before I posted up so I may have this some what figured out just want someone to check my thinking.
I want to run 100 amp service out to my pole barn I have 200 amp service at the house with room in the panel. I have 2" PVC run under ground with long radius sweeps. Run is about 250 ft
So from what I can tell I need to use 2/0-2/0-2/0-1 AL Mobile Home Feeder Wire.
I from what I can calculate this will give me voltage drop 6.6284 for a 2.7618% voltage drop. I believe I need to stay under 3% so I am good here.
I have a 100 amp panel from a friend who upgraded his service, so I just need to make sure the neutral bar is un-bonded.
I need to drive 2 ground rods connected by #6 bare copper.
So what have a missed or am I way off base.