There are many threads in this section of the forum asking about sizing 100 Amp subpanels, yet when I run the NERC calculator @ electrician2.com (NEC Table 310.15(B)(16) Conductor Size, OCPD, Voltage Drop, and Equipment Grounding Conductor Size Calculator), the calculated cable size (#1 Cu) is significantly larger than most recommendations on the forum.
Can anyone explain why the calculator is calling for #1 AWG cable, yet many electricians are recommending #2 or more typically #3/#4 cables for a 100 A subpanel? I know that you can replace the breaker with a 95 Amp and go down to #2, cable, but it seems like accepted practice is to run smaller gauge wire than what the calculator is calling for.
I've already run 2" conduit and I'm ready to go pull the permit. I usually work alone and pulling (3) #1 cables plus a #6 ground looks like quite a challenge, given the large number of junction boxes I have in the run. I suppose I could drop down to #2 and replace the 100 Amp breaker with a 95 Amp one, but that seems like I'm wimping out.
Thoughts?
Can anyone explain why the calculator is calling for #1 AWG cable, yet many electricians are recommending #2 or more typically #3/#4 cables for a 100 A subpanel? I know that you can replace the breaker with a 95 Amp and go down to #2, cable, but it seems like accepted practice is to run smaller gauge wire than what the calculator is calling for.
I've already run 2" conduit and I'm ready to go pull the permit. I usually work alone and pulling (3) #1 cables plus a #6 ground looks like quite a challenge, given the large number of junction boxes I have in the run. I suppose I could drop down to #2 and replace the 100 Amp breaker with a 95 Amp one, but that seems like I'm wimping out.
Thoughts?