Not mine, but a friends.

He has an older house at the end of an industrial district, only house on the street. The main high voltage is huge 3 phase awesomeness powering these factories. His house is fed with one line from this to a small transformer and I don't think there is a neutral back up on the pole, just one wire crosses the street and the guy/tension wire a few feet down the pole.

Transformer looks small, only a single house application.
Weatherhead and mast, to the meter, then to a disconnect, then 50 feet of SER to the panel through the walls of the house.

The 60amp sub is in the garage and when he welds or does some things the lights will flicker a little. Two ground rods.

I thought open neutral or something like that, turned on a hot plate full bore on a few different recepts and it wasn't reproduceable.

Put my meter on each leg while doing this and it was 120v +- 2v and the other was 116v or so.

It doesn't seem to be a grounding issue or a neutral issue except at the meter or pole... not sure how it works.

What else can I check or confirm?
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The 60amp sub is in the garage and when he welds or does some things the lights will flicker a little. Two ground rods.

I thought open neutral or something like that, turned on a hot plate full bore on a few different recepts and it wasn't reproduceable
Not saying there isn't a problem with an old electric system but 100A daisey chained for a long ways with welding or air comp on and the lights flicker a little?
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Not mine, but a friends.

He has an older house at the end of an industrial district, only house on the street. The main high voltage is huge 3 phase awesomeness powering these factories. His house is fed with one line from this to a small transformer and I don't think there is a neutral back up on the pole, just one wire crosses the street and the guy/tension wire a few feet down the pole.

Transformer looks small, only a single house application.
Weatherhead and mast, to the meter, then to a disconnect, then 50 feet of SER to the panel through the walls of the house.

The 60amp sub is in the garage and when he welds or does some things the lights will flicker a little. Two ground rods.

I thought open neutral or something like that, turned on a hot plate full bore on a few different recepts and it wasn't reproducible.

Put my meter on each leg while doing this and it was 120v +- 2v and the other was 116v or so.

It doesn't seem to be a grounding issue or a neutral issue except at the meter or pole... not sure how it works.

What else can I check or confirm?

First of all, a 120v/240v transformer will have 2 bushings/inputs. The second input is probably connected to a ground rod at the base of the pole. Its using the earth as a neutral/return path back to the substation. This setup isnt very common except in rural areas where substantial savings on wire can be had because only 1 wire is ran from pole to pole.

This type of system is called single-wire earth return:

http://en.wikipedia.org/wiki/Single-wire_earth_return

It wouldnt be a grounding issue since electricity, under normal conditions, doesnt flow on EGCs/grounds. The exception to this is the subpanel could be fed via a 3-wire feeder(2 hots and a neutral), the neutral developed a bad connection and electricity found an alternate path back to its source via a parallel conductive path between the garage and the house. However, the conditions u describe doesnt show to be a neutral issue. This is because when a neutral is bad you will see one leg(unloaded leg) with a higher voltage to ground or neutral and the other leg with a lower voltage to ground, both adding up to ~240v.

Is the welder 240v or 120v? how many input amps? What is the size of the feeder wire going to the garage and how long is it?

This leads to my next idea, which i go into below.

Voltage drops on one leg when load is applied. 120v with no load.

So the voltage only drops on one leg with a load and not the other leg while under a load?

Youre gonna have to track it down before calling the PoCo. What i would do is turn on the same load that it happens with, go to the main service panel, and measure the voltage between each leg and neutral and between both legs. If no drop then this tells u that the issue is somewhere in the feed going to the garage. Could be high resistance/bad connection, etc. If the voltage drop IS present at the main service panel, then this tells u that the issue is either in the service entrance wire in the mast, the PoCo's service drop, the transformer, or the high voltage feeder or neutral connection at the primary bushing of the transformer.

This happened to me one time. I had voltage drop on one leg that would cause some lights in the house to dim when I ran the garbage disposal. I left my meter probes clamped to the bus bar and neutral, set it for 'hold' on the 'min' reading and left it there over night. Voltage would drop as low as 100v on the bad leg. Called the PoCo, they came right out, discovered one of the splices(had 2 service drops spliced together at a pony pole) was REALLY HOT and had a bad connection. He added another splice without disconnecting the bad one and that fixed the issue.
 
Last edited:
OP
M

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
Electrician coming out tomorrow I guess to go through the meter and the disconnect.

I can't believe the neutral would be earth, but I see no other wires. I'll have to take some pics.

I'll let you know what the electrician discovers.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Electrician coming out tomorrow I guess to go through the meter and the disconnect.

I can't believe the neutral would be earth, but I see no other wires. I'll have to take some pics.

I'll let you know what the electrician discovers.

Why bother calling an electrician just uet. U could do the investigating yourself and save money.

And yes, the earth can be used as a neutral. Did u read the link i posted above?? Look at the primary bushings of the transformer which are typically on top. One of them connects to the single high voltage primary wire up top. The other bushing should connect to a bare wire that is stapled to the pole and runs down the pole to a ground rod at the base.
 
To avoid these ads, REGISTER NOW!

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
It's not his money, this is for a friend. And if you are not comfortable playing with service lines, it is best to call someone.
 
OP
M

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
Electrician friend confirmed what I did. 115v on one leg. Called DTE (LPC) to come investigate. Old transformer and **** connections. Yes Wylie I read what you said and it's spot on.
 
OP
M

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
Ok, looks like a tree limb at one point fell on the overhead lines and loosened the connections at the connection to the service.

Go figure!
 
Joined
Feb 27, 2014
Messages
568
Why bother calling an electrician just uet. U could do the investigating yourself and save money.

And yes, the earth can be used as a neutral. Did u read the link i posted above?? Look at the primary bushings of the transformer which are typically on top. One of them connects to the single high voltage primary wire up top. The other bushing should connect to a bare wire that is stapled to the pole and runs down the pole to a ground rod at the base.

:eyecrazy:
 
OP
M

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
I'm not 100% but I think he said 124v on one and 106v on the other or something like that. He said the difference was bad enough. He does a lot with the poco I guess.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You got to wonder how many zillion connections like that there are, they are not uncommon. Someo f this has been in service a long time.
 