Cb-man
Well-known member
so last year I ran #2 copper to an existing barn and put up a 100A panel. feed from a disconnect right out of the meter then 200 ft to the barn.
thinking I was going to finish this barn.
Well this year I went and built a new pole barn. I'm trying to figure out the best way to get another 100A service to it.
I no where need 100 amps in the old barn now. only lights and a garage door opener.
the new barn is about a 125ft run from the panel in the old barn. if I run #2 copper from the panel to the new barn voltage drop wise on #2 looks like I will be limited to 70 Amps.
any body have any suggestions on what to do?
the new barn with be more lights and outlets. a 2 post lift. 220v compressor on a 30a breaker and only a 120v welder for now. obviously not all used at once.
easiest to me seems to be throw a breaker in the old barn panel and feed it that way but I am curious as to the wire size that will fit in a 100a breaker
thinking I was going to finish this barn.
Well this year I went and built a new pole barn. I'm trying to figure out the best way to get another 100A service to it.
I no where need 100 amps in the old barn now. only lights and a garage door opener.
the new barn is about a 125ft run from the panel in the old barn. if I run #2 copper from the panel to the new barn voltage drop wise on #2 looks like I will be limited to 70 Amps.
any body have any suggestions on what to do?
the new barn with be more lights and outlets. a 2 post lift. 220v compressor on a 30a breaker and only a 120v welder for now. obviously not all used at once.
easiest to me seems to be throw a breaker in the old barn panel and feed it that way but I am curious as to the wire size that will fit in a 100a breaker