Power from the street comes to a pole on my property, through a pole-top disconnect, then to the house. Folks here recommended the best way for me to get power to my shop would be to splice into the load side of the pole-top disconnect. Power company says I have 200A service to the house (150A panel in the house) and can send 100A to the shop.

What size/type of wire do I need to be able to provide a full 100A to the shop? I know A lot of folks use 2-2-2-4 MHF and a 90A breaker, but I'd like the full 100A unless it's significantly more expensive.

Edit: The wire run will probably be around 150ft.
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,777
Location
NW Iowa
#1 is 100A but you might not find it it direct bury. 1/0 is the next size larger and is common
 
OP
S

Smiles79

Well-known member
Joined
Feb 15, 2018
Messages
290
Location
Northwest Missouri
OP didnt say anything about direct bury

I would just bury some conduit and use individual conductors of #1 AL xhhw with a #6 AL for EGC.
Thanks! So that will allow me to feed 100A instead of 90? And I can use xhhw for the whole run as long as it's in conduit?

Looks like it's about $0.12/ft more expensive than MHF on wireandcableyourway. Only $18 over the whole run. Worth it!
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
You could reduce the neutral conductor to #3. (if your local codes permit.)
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Thanks! So that will allow me to feed 100A instead of 90? And I can use xhhw for the whole run as long as it's in conduit?

Looks like it's about $0.12/ft more expensive than MHF on wireandcableyourway. Only $18 over the whole run. Worth it!
PVC conduit is no longer cheap like it was in the past, but pipe is always better then direct burial, conduit is a one time insurance policy.
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,921
Location
Richmond, VA
Thanks! So that will allow me to feed 100A instead of 90? And I can use xhhw for the whole run as long as it's in conduit?

Looks like it's about $0.12/ft more expensive than MHF on wireandcableyourway. Only $18 over the whole run. Worth it!
Yes, 100a is good with #1.

If you really expect to pull 100a, you should go up a a size as voltage drop will be a factor at that distance
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,921
Location
Richmond, VA
Yeah, it looks like 1/0 would be the proper size. What size does the egc need to be?
I believe #4. You can use #1 for a neutral.

This is where scope creep costs money. Most single person shops are fine with a 60a feed, which #2 can do easily at that distance
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,511
Location
VT
Looks like it's about $0.12/ft more expensive than MHF on wireandcableyourway. Only $18 over the whole run. Worth it!

Check your local supply houses. As a walk up customer mine just came in lower then that site, even lower once shipping was factored in.
 