As the title states...looking to run a 100A service from my 200A panel. Length is appx 140ft. Planned to use 1/0 Aluminum URD however thats not going to connect to the breaker. Do I bug on #2 copper after I transition thru the LB or is there a small box that has lugs similar to service feed where I can transition inside for same purpose? Thx much!
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
For 100A @ 140ft you can use #1 Al. Also you need to transition to a different type wire for the inside, the URD has to be terminated on the outside. If you can get by with a 90A feed then use 2-2-2-4 (MHF) Mobile Home feeder. The MHF can be installed inside, but does need to be in conduit.
 
OP
6

64duece

Well-known member
Joined
Feb 15, 2009
Messages
47
Thanks for the tip. I have a Tig machine on a 50A breaker and if I'm doing aluminum it'll use it. We have a compressor and lifts..mostly worried about in-rush current if I'm welding and a buddy is using an air tool or lift. Ill spend a few extra bucks for the few additional Amps of headroom. What do you recommend for making the outside transition? I planned to use LBs on both house and shop.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
As pattenp mentioned, URD cannot be used anywhere inside a building, unless it has other markings on it that do allow its use inside (which is doubtful with URD). The URD does not have the fire resistance required for inside use.

Charles
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
To switch to something like SER for the inside you will need to use a large junction box outside for the splice. A PVC box that's 8X8X4 should work. A LB body will not have the needed volume for doing a splice.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,106
Location
SE MI
For 100A @ 140ft you can use #1 Al. Also you need to transition to a different type wire for the inside, the URD has to be terminated on the outside. If you can get by with a 90A feed then use 2-2-2-4 (MHF) Mobile Home feeder. The MHF can be installed inside, but does need to be in conduit.

Another endorsement for MHF. To clarify, MHF does NOT require a conduit when buried. Conduit is only required inside. If your conduit goes into the ground next to a building, use Schedule 80 pipe. A good string trimmer will breaker Schedule 40 (standard) pipe.
 
OP
6

64duece

Well-known member
Joined
Feb 15, 2009
Messages
47
Thx again...this info is very helpful. I'm gonna go over this info with my supply house and see what we can come up with. Can't wait to get juiced up! Lol
 