100A Sub Panel

j2ritt

New member
Joined
Sep 26, 2023
Messages
2
Hi,

I'm running electric to my shop. The building is around 300' from my house, maybe a little more from panel to panel.

I am in the process of having a new septic system installed which basically requires us to dig a trench from the house to within 20' of the shop. So, the plan is to bury conduit in the trench for the septic system at the same time.

I'd like to run 100A service. I haven't done load calculations, but my thought is I'd rather spend a little extra now than potentially have too much draw in the future. Future plans involve a heatpump split unit, welder, etc. so I just don't want to run into too much draw down the road if I can avoid it.

Since I need to run conduit anyways - I was considering using XHHW-2 AL 2/0 runs, instead of MHF since it's a little cheaper and more pliable and will be enclosed in conduit either way. Thinking I need (3) runs of XHHW-2 AL 2/0 for 2 hots and a neutral + (1) run of #1 AL for ground. Does that sound right?

thanks in advance
Josh
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
It's best to calculate full anticipated loads. At 300ft a total load of 80A will be a little over the recommended 3% voltage drop using 2/0 Al.
 
OP
J

j2ritt

New member
Joined
Sep 26, 2023
Messages
2
It's best to calculate full anticipated loads. At 300ft a total load of 80A will be a little over the recommended 3% voltage drop using 2/0 Al.
ok, after some rough calculations I wouldn't expect load to be more than 50amps at any given time. Even that may be high, I was imagining peak load time would likely be if an AC is running while I'm using a welder. Other than that it would be 1 or 2 woodworking tools being us at the same time and maybe a split AC unit if I put one in eventually.

Also - I remeasured the distance and the run will actually be 250'

Looking at Southwire's Voltage Drop Calc it looks like 80amps is within the limits of 2/0 AL for that run.

So - I think what I need is:
2/0, 2/0, 2/0, #6 wires with an 80 Amp (2-Pole) Breaker

Sound reasonable/logical?

appreciate the help
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
I'd downsize the neutral. 2/0 is necessarily large.

I don't know if you will be able to land a 2/0 on an 80a breaker. Either way, I'd probably just do a 100a.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,498
Location
SE MI
Classic GJ OVERKILL !!!

The MOST COOMON feed to a "one man" shop is 60A. You can easily run A/C-heat pump and a welder. Worst case maybe a plasma cutter because you need to have the compressor on at the same time. Turn off the A/C.

With a 60A feed, you can probably get away with 1/0 or maybe even 2.

IT'S YOUR $$$$ !
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,324
Location
Coastal NJ
Sometimes folks anticipate an EV charger in the future so larger services are considered. I don't expect to have an EV but I suppose the next owner of my place might/will. Not looking to start an EV debate. And yes I know you can charge at lower rates than 48A. Given the push for electrification of everything, a "one man shop" is still a building that may in the future have greater load.

I ran into the POCO man changing out the meter on the 3200 sf house next door. It has 320/400A service. He commented that most of the new houses in the area have that size service. And that same house has natural gas heat, water heaters and cooking. The largest load in that place are the (2) three ton AC units and the hot tub.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Sometimes folks anticipate an EV charger in the future so larger services are considered. I don't expect to have an EV but I suppose the next owner of my place might/will. Not looking to start an EV debate. And yes I know you can charge at lower rates than 48A. Given the push for electrification of everything, a "one man shop" is still a building that may in the future have greater load.

I ran into the POCO man changing out the meter on the 3200 sf house next door. It has 320/400A service. He commented that most of the new houses in the area have that size service. And that same house has natural gas heat, water heaters and cooking. The largest load in that place are the (2) three ton AC units and the hot tub.
320a is standard in my neighborhood, and we have gas.

While people might want an EVSE in the future, charging is ge really done overnight when not many high draw tools are in use. I really don't think it changes the math in 98%+ of cases
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,324
Location
Coastal NJ
320a is standard in my neighborhood, and we have gas.

While people might want an EVSE in the future, charging is ge really done overnight when not many high draw tools are in use. I really don't think it changes the math in 98%+ of cases
What drives the move to 320A with gas service in place?
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
What drives the move to 320A with gas service in place?
My guess it's a mix of "just because" and it's a highlight on the listing. Larger houses need lots of circuits, so it either needs a massive 200a panel or two 200's. If you're putting in two 200's, might as well go 320a.

My panels are mostly full but even with all three ac's and the pool heater running, I wouldn't hit 200a of draw
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,217
Location
NJ
My guess it's a mix of "just because" and it's a highlight on the listing. Larger houses need lots of circuits, so it either needs a massive 200a panel or two 200's. If you're putting in two 200's, might as well go 320a.

My panels are mostly full but even with all three ac's and the pool heater running, I wouldn't hit 200a of draw
It becomes a notable selling point vs. just having to spend a lot of $$ to properly protect the 200A SE cable and meter that gets no mention. Two panels fed off of a 320A meter pan with dual lugs is easier to install.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,186
Location
Modesto, CA
ok, after some rough calculations I wouldn't expect load to be more than 50amps at any given time. Even that may be high, I was imagining peak load time would likely be if an AC is running while I'm using a welder. Other than that it would be 1 or 2 woodworking tools being us at the same time and maybe a split AC unit if I put one in eventually.

Also - I remeasured the distance and the run will actually be 250'

Looking at Southwire's Voltage Drop Calc it looks like 80amps is within the limits of 2/0 AL for that run.

So - I think what I need is:
2/0, 2/0, 2/0, #6 wires with an 80 Amp (2-Pole) Breaker

Sound reasonable/logical?

appreciate the help
the online calculators are notoriously wrong. (for southwires i wonder why :sneaky: )... i posted the equation in the FAQs if you want to calc it yourself and possibly save some money on wire... im too lazy to calc it right now... also need to run out the door...
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,324
Location
Coastal NJ
It becomes a notable selling point vs. just having to spend a lot of $$ to properly protect the 200A SE cable and meter that gets no mention. Two panels fed off of a 320A meter pan with dual lugs is easier to install.
The selling point factor was also behind my earlier comment in post #7

Selling point math is different than a load calc.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,321
Location
Illinois near St. Louis, Missouri
1/0 at 250 ft and 80A give 3.33% voltage drop. Close enough on voltage drop I say. 100A is really big for a shop unless you have some really big equipment and/or multiple people working. You could downsize the neutral but some areas don't allow that.

320A service is very common in this area too and most homes have gas heat. Does make wiring a little less crowded in the panels with two 200s.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,217
Location
NJ
Southwire sells what the name implies... wire. It's based on a conductor temp of 60C.
I've found this one>>>>> https://www.calculator.net/voltage-drop-calculator.html to be fairly accurate.
The app has been upgraded to allow to insulation temp selection. BTW, before this change was done, the app had technical notes indicating they were using 60C ampacities for #1 and smaller b/c of NM-B.

 
To avoid these ads, REGISTER NOW!