Hey all, I have done a bunch of searching but I thought I'd throw this out because it is a bit different.
I just put on an addition and replaced my attached garage. I currently have 100Amp service and I'm going to do an upgrade to 200amp.
My thought is to leave my current 100Amp panel untouched due to potential issues with having to mess with current house wiring. I would rather leave that for another time. My current Idea is to use this 200 Amp disconnect with 2x100amp breakers.
I have two 125 amp lug centers, one for a 100amp sub in the basement addition and then use the other for a 60amp in the garage.
Now, unfortunately the way the grade changes and structural I don't have a clear path from my existing panel to my sub location(s). Mainly a huge lvl blocking path. I don't want to drill the LVL. I could get around it with tighter bends.
I am wondering if I could use the 4/3 MC-Copper cable referenced in the attached file. What I see is that it is rated @ 95 AMP in the 90 degree column. My understanding is that you would be able to step up to the next size breaker or 100 AMP in this case. Or is the 90 degree column only used for derating in this instance.
MC-copper pdf link.
The MC would not be in insulation.
Thanks
I just put on an addition and replaced my attached garage. I currently have 100Amp service and I'm going to do an upgrade to 200amp.
My thought is to leave my current 100Amp panel untouched due to potential issues with having to mess with current house wiring. I would rather leave that for another time. My current Idea is to use this 200 Amp disconnect with 2x100amp breakers.
I have two 125 amp lug centers, one for a 100amp sub in the basement addition and then use the other for a 60amp in the garage.
Now, unfortunately the way the grade changes and structural I don't have a clear path from my existing panel to my sub location(s). Mainly a huge lvl blocking path. I don't want to drill the LVL. I could get around it with tighter bends.
I am wondering if I could use the 4/3 MC-Copper cable referenced in the attached file. What I see is that it is rated @ 95 AMP in the 90 degree column. My understanding is that you would be able to step up to the next size breaker or 100 AMP in this case. Or is the 90 degree column only used for derating in this instance.
MC-copper pdf link.
The MC would not be in insulation.
Thanks