100amp upgrade

camaro0991

Well-known member
Joined
May 4, 2011
Messages
127
Hey all, I just upgraded my house to 200 amp service, so now I'm going to upgrade the garage from 50 to 100amps. My issue is i need to know what gauge of wire for the main cable I need to run from my panel in the house to my sub panel out in the garage. Its probably about a 200 foot run or so, maybee more(haven't had time to measure out out yet, but its a decent run). Any help would be appreciated.
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Quite a few people are using #2 AL mobile home feeder on a 90 amp breaker. It's readily available and fairly inexpensive.

You can search "mobile home feeder" on here and find more info.
 
To avoid these ads, REGISTER NOW!

VHF

Well-known member
Joined
Oct 27, 2008
Messages
420
Location
NW Wisconsin
If using CU (copper) then #3 would be the minimim size for a 100A feeder, but at around $1.35/foot for 600' that would be pricey. Also, at 200' you might need to step up to #2 to reduce voltage drop.

Whether you use AL or CU make sure you run 4 conductors (the ground can be smaller.)
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,788
If using CU (copper) then #3 would be the minimim size for a 100A feeder, but at around $1.35/foot for 600' that would be pricey. Also, at 200' you might need to step up to #2 to reduce voltage drop.

Whether you use AL or CU make sure you run 4 conductors (the ground can be smaller.)

If you increase the ungrounded conductor size, the grounding conductor per NEC 250.122(B) must be increased proportionally. It does not matter what the reason is it still has to be increased.
 