What's the difference between thhn and the thwn you recommended? Can they both carry the same amperage just one waterproof ?youre reading the wrong column
90*c is for derating only.
90a is not excessive.
NEC code allows upto 250% of NEC FLC table current for inverse time breakers.
50*2.5= 125a.
The 70a or 80a may trip but try it and see.
This is because motors have whats called in rush current that can be 4-8x FLA for fractions of a second.
Make sure you use #6 THWN.
#6 NM-b is too small.
A bigger question is whether your PoCo will allow a 10HP motor.
Most have limits on HP.
What size service do you have?
Are you the only one on the transformer?
Are you at the end of the line?
A 10HP may cause considerable voltage sag on the service. If youre on a shared transformer, you may cause issues for your neighbors as well..