Putting new electric in my garage and I’ve got a couple of spots where I am going to put dedicated 110 outlets for a fridge and air compressor.

As these would be dedicated 20A outlets, I started thinking that if I run them with 10ga, wire instead of 12ga and put them in a quad box, I could easily upgrade those outlets to 220 in the future if needed as long as I leave a breaker slot open next to each.

Does that sound reasonable or am I missing something?
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
#12/20A/240v circuits are very useful in my shop. It's all my compressor and welder need.
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,824
Location
Niagara Region, Ontario, Canada
as noted, wire gauge doesn't determine voltage , it determines amps . a run of 14/2 is capable of feeding 240 but is limited to 15amps
what sort of amperage do you need for your 240 circuit?
 
OP
K

kolky

Active member
Joined
Dec 30, 2013
Messages
36
Location
St. Louis, MO
Sorry should have stated 240.

I was thinking 10ga in case I needed to go up to 30A 240 and because I ended up getting some 10ga wire on Amazon a while back when they had it for $35 for 50ft. Some of the things I could see using that in the future would be an electric car charger, large compressor or welder.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
If you are running new electric, then you should have a panel large enough for future add on's. Run your 120 volt receptacles and run some for 240 volt receptacles now or down the road. The gauge of wire has nothing to do with voltage
 

karoc

Well-known member
Joined
Dec 19, 2017
Messages
1,994
Location
Hemphill Tx
Like my ole father inlaw us to say “ Better to have it,than to want it” 10 will give you more flexibility
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
I agree that you should build it for future growth and flexibility. Another consideration for you is what you are putting on your walls. I did 1/2” plywood with tech screws. When I added the solar last year it took me about 15 minutes to remove the two sections of wall necessary to access the interior of the wall and add the combiner panel, etc. It took about 15 minutes to close back up. I’m kinda slow and didn’t anticipate my needs properly. Being able to access the interior of the walls has really helped me out. With plywood prices where they are you may only do sections of the wall.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
Most 15-20a devices won't take #10 so you have to pigtail it down.

Upsizing is never-ending. If you go #10, you'll get a machine that needs #8.

I wire in what I need when I actually need it. Saves a lot of money.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Run some flexible conduit through the walls, through the top plate, or both.
Then no matter what your needs in the future you'll be covered.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
What I did in my shop is run #12 MWBC's on a 2-pole breaker. Then wherever I have a box, I can wire a 120 or 240 receptacle as needed.

Doesn't work with gfci's of course, but I don't need or require them.
 

hippie2cams

Well-known member
Joined
Jul 15, 2012
Messages
384
Location
Huffman,TX
When I built mine I had the electrician run all the basic wiring before insulating, then install surface mount box so addons could be run through conduit.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
When I built mine I had the electrician run all the basic wiring before insulating, then install surface mount box so addons could be run through conduit.
Yes, this exactly. If you are having finished walls, then run some flexible conduit from the panel to some surface mounted boxes. Then you can always add on to the boxes with conduit and pull in circuits later.
 

Citation

Well-known member
Joined
Jan 20, 2016
Messages
3,212
Location
Indy
I get the idea but I think I would do it differently. For example, currently you have a 120V compressor but in the future you might need a bigger compressor. So the 10A wires that currently feed a standard 120V outlet could later be changed over to a 20A, 240V outlet (bigger compressor, welder, electric car charger etc). It could be handy but really if you think you might want a 240V outlet in the future, run the wire now even if you just wire it into a box with a cover plate. If you have the panel space, put in the breaker but leave it off with a tag or something. If you really can't just leave a 240V line terminating in a box in the wall then sure, use the 10G wire for this outlet. You could change it later.
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
There are 2 ways of protecting MWBCs.
You can install a 2 pole GFCI breaker or where you have 120V circuits install separate GFCI receptacles
Agreed, I was thinking of the receptacles.

Regardless, I require neither one.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,916
Location
Coronado, CA
110/120/125 ?, I am one of those Dinosaurs who is slowly adapting to the latest permutations of our version of the “English” language.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
110/120/125 ?, I am one of those Dinosaurs who is slowly adapting to the latest permutations of our version of the “English” language.
Thats because you have it wrong …..it’:

110/115/120

We have not up the ante to 125 yet.😀
 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
just make sure the wire feeding you sub panel is big enough. Why not put in a nema 6-50 outlet to feed a welder now. Also, get a compressor that will take the higher voltage and wire it that way for quieter start ups.
 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
Please explain why the start ups would be quieter.
Start ups are easier running the motor on higher voltage, there is less inrush current. On lower voltage when the compressor kicks on you get the typical lights dim, low growl of the motor, then it comes up to speed. With the higher voltage the motor just turn on.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Start ups are easier running the motor on higher voltage, there is less inrush current. On lower voltage when the compressor kicks on you get the typical lights dim, low growl of the motor, then it comes up to speed. With the higher voltage the motor just turn on.
If properly wired for the load at the voltage used a duel voltage motor will start and run the same on 120V as on 240V. The issues you give are due to voltage drop from an inadequate supply and has nothing to do with 120V vs 240V in itself.
 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
I would have to disagree with you from my personal experience. A compressor plugged in at an outlet right at the SE running low voltage starts up the same as it does 300 feet away in my shop. Transformer is 50’ from SE. so unless you think the service cables or transformer are undersized (they are not) then I would say that the higher inrush current on the lower voltage wiring was responsible. YMMV.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
You would think so, but every thing I have ever changed from 120 to 240 starts up faster and easier on 240 (Or are we up to 245-250 yet?)

I wonder if there is math to support that. i always thought you went 2XX volt to reduce wire size for same KW.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I would have to disagree with you,...... I would say that the higher inrush current on the lower voltage wiring was responsible. YMMV.
That's what causes voltage drop which is what I was saying. The wiring is undersized to handle the inrush current. Just to generically say a motor runs better on 240V vs 120V without stating other mitigating variables is inaccurate.
 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
What I am saying is that plugged directly into the source it still does it, so is it really a mitigating factor? Or is it just the way it is?
 

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,577
A lot of dual voltage consumer grade compressors come with and undersized cord. That may be the limiting factor on 120v.
 

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,058
Location
The romantic hills of central Umbria, Italy,
But wait, my current electrical line voltage is 113.31 ± .2%... anything else is WRONG and NOT IN AMERICA...

Because even though we ALL know what is meant by 110-220 or 120-240 or 117-234... we still have to show we are smarter than y'all...

🎣
 