I'm doing some temporary wiring for lighting in my garage. Existing lights are wired with 14/2 and I need to add two more lights to the circuit, but I only have 12/2 wire left over from another project. Can I mix the two different gauges on the same circuit without any issue? All of the lights will be re-wired in the next two weeks or so. I just want to get a feel for how bright it will be out there with the two additional lights.
 
To avoid these ads, REGISTER NOW!

jdm5

Well-known member
Joined
Jan 1, 2012
Messages
281
Location
CT
The existing lights are 14/2 - that means they should be connected to a 15 amp breaker. Assuming so then it’s no issue to use 12/2.

If it’s connected to a 20a breaker you have an existing problem.
 