I'm working on a circuit for a steam humidifier. Aprilaire calls for a 25A, circuit, so I was going to run 10/2 NM-B, but I was wondering if 12/2 MC would work since the conductors are labeled thhn.
If I have this right, despite 12/2 MC using thhn, which has a 25a rating in the 75 degree column, I am limited to 20a per 240.4(D) unless the installation meets an exception in 240.4(G).
So, is a steam humidifier, which is installed at the air handler and can't function without the hvac system, "Air-conditioning and refrigeration equipment"? Or does that only provide for equipment with motors?
If I have this right, despite 12/2 MC using thhn, which has a 25a rating in the 75 degree column, I am limited to 20a per 240.4(D) unless the installation meets an exception in 240.4(G).
So, is a steam humidifier, which is installed at the air handler and can't function without the hvac system, "Air-conditioning and refrigeration equipment"? Or does that only provide for equipment with motors?