12/2 MC for 25a circuit

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
I'm working on a circuit for a steam humidifier. Aprilaire calls for a 25A, circuit, so I was going to run 10/2 NM-B, but I was wondering if 12/2 MC would work since the conductors are labeled thhn.

If I have this right, despite 12/2 MC using thhn, which has a 25a rating in the 75 degree column, I am limited to 20a per 240.4(D) unless the installation meets an exception in 240.4(G).

So, is a steam humidifier, which is installed at the air handler and can't function without the hvac system, "Air-conditioning and refrigeration equipment"? Or does that only provide for equipment with motors?
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,212
Location
NJ
The exceptions in 240.4G are for the circuits supplying motor driven Air-conditioning and refrigeration equipment...i.e. compressors, fans.

A steam humidifier is a mostly a resistive load and probably considered a continuous load. If so, then circuit conductors and ocp needs to be @ 125% of FLAs.

What do the installation instructions spec?
 
OP
M

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
The exceptions in 240.4G are for the circuits supplying motor driven Air-conditioning and refrigeration equipment...i.e. compressors, fans.

A steam humidifier is a mostly a resistive load and probably considered a continuous load. If so, then circuit conductors and ocp needs to be @ 125% of FLAs.

What do the installation instructions spec?
Its a 16a draw, specifying a 25a circuit, hence that being what I'm designing for. Initially, I saw the 16a draw and was planning on 20a to accommodate the 125% sizing but they call for 25a for some reason, so that's what I'm doing.

Its not a long run, so it doesn't matter much anyway, just trying to learn and understand options.

The panel is close by and within sight, but I'm going to install a 30a dual pole switch at the unit for a disconnect. I'd rather not be using the breaker for service and shutting it down in the summers
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,212
Location
NJ
Based on the above info alone, it should be ok on a 12ga nm-b/ 20a cb. Possibly they are considering voltage drop and indirectly forced the 20A ckt to requiring #10's/25-30A.

Pic of nameplate?
 
OP
M

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Based on the above info alone, it should be ok on a 12ga nm-b/ 20a cb. Possibly they are considering voltage drop and indirectly forced the 20A ckt to requiring #10's/25-30A.

Pic of nameplate?
Edit... You beat me to it.

I dont have it on hand, but the manual stage "16A +/- 10%", so that must be what is pushing it to a 25 circuit.
1000003343.jpg
 
OP
M

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Post the nameplate anything else is guessing
As has already been posted, I don't have it.

But that isn't really relevant. My question was if 12/2 MC could be breakered at 25a for the application. Feels like that is sorted
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,323
Location
Coastal NJ
How many gallons are needed? Seems it can cover a variety of outputs. I suppose I'd also wire it for the max, but the size of the house and how air tight it is determines gallons per day requirement.

1701970357563.png
 
OP
M

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
How many gallons are needed? Seems it can cover a variety of outputs. I suppose I'd also wire it for the max, but the size of the house and how air tight it is determines gallons per day requirement.

1701970357563.png
I have no idea, that's part of why I want to go max. If it I was repuposing an existing circuit, I'd cut it back, but I have to run one anyway, and I happen to have a two pole 25 on hand, so the incremental cost is actually only $40 over 12/2 NM-B and the 11.5a setting.

Changing it to that lower output is just a dipswitch, so if I find the higher level excessive, I can drop it back to see if it saves money or manages humidity better
 
To avoid these ads, REGISTER NOW!

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,127
Location
Fernley, Nevada, about 30 miles east of Reno.
I'm working on a circuit for a steam humidifier. Aprilaire calls for a 25A, circuit, so I was going to run 10/2 NM-B, but I was wondering if 12/2 MC would work since the conductors are labeled thhn.

If I have this right, despite 12/2 MC using thhn, which has a 25a rating in the 75 degree column, I am limited to 20a per 240.4(D) unless the installation meets an exception in 240.4(G).

So, is a steam humidifier, which is installed at the air handler and can't function without the hvac system, "Air-conditioning and refrigeration equipment"? Or does that only provide for equipment with motors?

Article 440 of the NEC covers air conditioning and refrigeration equipment.

440.1 Defines the scope of the article and it states, basically, that it applies to motor driven equipment.

The exceptions to 240.4(G) (overcurrent protection) apply to part III and IV of 440 and those sections apply to motors.

Based on the above, it seems to me that the humidifier would be a separate piece of equipment that is controlled by the HVAC and not part of it as defined by 440.

The actual reality of it is that 12/2MC with a 25 amp breaker would handle 16 amps continuously for a very long time.
 
Last edited:

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
OP
M

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Article 440 of the NEC covers air conditioning and refrigeration equipment.

440.1 Defines the scope of the article and it states, basically, that it applies to motor driven equipment.

The exceptions to 240.4(G) (overcurrent protection) apply to part III and IV of 440 and those sections apply to motors.

Based on the above, it seems to me that the humidifier would be a separate piece of equipment that is controlled by the HVAC and not part of it as defined by 440.
Thanks
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,212
Location
NJ
The actual reality of it is that 12/2MC with a 25 amp breaker would handle 16 amps continuously for a very long time.