12-3 wire on a 30 amp breaker??

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
Don’t think that is good
The ice storm has put a hurting on power lines
We have been out of power since early Saturday morning
I have a generator
My next door neighbor finally found one generac 6500-8000
They just moved in a year ago
The setup his house has is 12-3 wire connected to a 30amp double pole breaker in house panel
4 prong plug on other end that plugs into generator
Pretty sure he should have at least 10-3 wire
It’s not the flat yellow wire used in houses
It’s white insulation
My guess is it has been like that since the house was built in 1999
Should he be careful about what he powers
 
To avoid these ads, REGISTER NOW!

esvee

Well-known member
Joined
Dec 28, 2014
Messages
171
Location
Portland, OR
It depends.

That breaker is probably made for an A/C unit specifically, which would fall under NEC, Art.440, Section III. 430.22E also specifies certain motors requiring a 30A breaker but can be wired with a 12AWG conductor.

https://www.mikeholt.com/mojonewsar...ning-and-Refrigerating-Equipment~20040102.htm

To make that breaker support whatever he wants to plug into it with the assumption there is 30A on the other side then yes the conductors should be 10AWG.
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,679
Location
Maine
There was time when Romex was one color, white, so don't go by color of jacket to know if its 10 or 12 gauge.
 