I have seen this done on some large shops, not alot of information about remote manifolds here. I think it makes sense in alot of applications. My shop will be 60x80 and if i want to have my boiler in the corner of the shop i will be using 160 feet of my 300 foot run just to reach the other end. This doesn't work well if I want to have zones on the other end. I think remote manifolds would make the layout easier. I am still looking into this. I had one company suggest 7/8 tubbing for my layout but a remote manifold with 1/2 seems to make more sense. could I supply the manifold with 1inch pex through the slab?
There is nothing unusual/complex/special/difficult .... pick your term -- about increasing the distance between the boiler and the manifold.
Pick the correct size pipe/ insulate and connect.
This is for copper.
1 1/4 pipe was often used for primary as it will allow up to around 180k BTU's -- you are only at around 100k for 1". The friction loss is 1/2 w/ the larger pipe. This was required for the proper flow through the boiler .... 1 1/4 is going to be in the 16 gpm and 1" is only a bit more than 10gpm.
If you look you will see different manifolds have different GPM --- 3/4 and 1" ... it all depends on the BTU's needed for that zone and the flow required to get those BTU out to whatever you are trying to heat.
With tighter buildings and more accurate heat load matching -- and manufacturers making smaller boilers 1" is often now enough. That's all you need for a 65k BTU boiler. But, it's still a question of resistance out to the manifold.
The tables are all available.
With PEX going out -- be careful. 5/8 and 3/4 pex is only 3.3 and 4.6 respectfully GPM ..... not going to be enough for most systems. 1" pex is going to get you into the 7.5 range .. still may not be enough.