120 to 240 conversion

mendozer

Well-known member
Joined
Oct 2, 2015
Messages
141
I got some ceiling mounted infrared heaters and in one room I wanted to use the wiring from a wall cadet heater to power it. The heaters are 240v, but can be 120 as well (just draw more that's all). But I was thinking...it only demands 12 gauge wire because of the amp draw at 240...can I just route the wires in the breaker panel to two slots, convert that line to 240 and use the white wire as a hot? That's bascially what the new wire runs are going to be so I don't see anything wrong with this.
 
To avoid these ads, REGISTER NOW!
OP
M

mendozer

Well-known member
Joined
Oct 2, 2015
Messages
141
i'll hav to double check the outlet in that room. the panel labels it as only going to the cadet heater but i'm gonna check because the previous owner did other weird things so i wouldn't put it past him
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
Just be sure to re-identify the white wire with a few inches of black electrical tape on both ends.

I'm sure the resident electricians will let us know if re-identification is required, or not.... I do it for good measure. (and because a friend of mine, who is a Master electrician, made me do it on several of my projects years ago. lolol)
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
I got some ceiling mounted infrared heaters and in one room I wanted to use the wiring from a wall cadet heater to power it. The heaters are 240v, but can be 120 as well (just draw more that's all). But I was thinking...it only demands 12 gauge wire because of the amp draw at 240...can I just route the wires in the breaker panel to two slots, convert that line to 240 and use the white wire as a hot? That's basically what the new wire runs are going to be so I don't see anything wrong with this.
Are these really dual voltage rate heaters? what is the make and model? unless youre rewiring how the elements are connected, they will not draw more power. a resistive load actually draws less power at lower than rated voltage.
 

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,098
Location
Fernley, Nevada, about 30 miles east of Reno.
If the heater is actually 120 or 240, it'll have 2 separate elements, both will be 120.

For 120 input, they will be connected in parallel, 240 will be a series connection.

On the nameplate, it will give 2 amperages, the higher one will be for the 120 connection, the lower will be half as much and be for 240.

If the heater is 240 only and it is supplied with 120, it'll draw 50% of the current and you'll get 25% of the heat. And if has a fan, it will turn slowly and eventually burn up.
 
To avoid these ads, REGISTER NOW!

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,098
Location
Fernley, Nevada, about 30 miles east of Reno.
I got some ceiling mounted infrared heaters and in one room I wanted to use the wiring from a wall cadet heater to power it. The heaters are 240v, but can be 120 as well (just draw more that's all). But I was thinking...it only demands 12 gauge wire because of the amp draw at 240...can I just route the wires in the breaker panel to two slots, convert that line to 240 and use the white wire as a hot? That's bascially what the new wire runs are going to be so I don't see anything wrong with this.

If the heater is actually 240 volts, then yes, you can indeed use a 12/2 for it. As noted, tape the white with just about any color other than gray or green. Black is fine.

Also, us a 2 pole breaker, not 2 single pole ones.
 

johnre

Well-known member
Joined
Dec 1, 2016
Messages
1,058
Location
Portland, OR
Just be sure to re-identify the white wire with a few inches of black electrical tape on both ends.
If the heater is actually 240 volts, then yes, you can indeed use a 12/2 for it. As noted, tape the white with just about any color other than gray or green. Black is fine.
Am I the only one here who thinks the H2 connection should only be relabelled red?

Because black is already being used for H1.

This is the way 12/2G Romex already comes colored for 240 V wiring..
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
Am I the only one here who thinks the H2 connection should only be relabelled red?

Because black is already being used for H1.

This is the way 12/2G Romex already comes colored for 240 V wiring..
There's nothing wrong with labelling it black. Or red, blue, brown, orange, yellow, pink, or purple. As long as it is marked to keep the next guy from thinking it's a neutral, it's ok.
 
OP
M

mendozer

Well-known member
Joined
Oct 2, 2015
Messages
141
i wired it up today. Heater will go on tomorrow. It comes set up for 240 from the factory but the infrared heater can be 120 also. it's the same 750W unit, just a different pigtail. So i assume it just draws amps differently. It's a solaray-d heater. And yes i labeled white to black tape and even wrote "240" on the romex sheath in the wall and the EMT box. I kind of like this EMT stuff. Grounded it from the romex right to the box and didn't have to run the ground wire in the conduit.
 
OP
M

mendozer

Well-known member
Joined
Oct 2, 2015
Messages
141
got it up and working. I BARELY had enough distance for the existing hot/neutral (now hot) lines in the panel without wanting to rearrange things. The conduit part worked out nicely but I forgot that the EMT box was to be surface mounted and i cut a hole before i started so I had to modify the inside of the wall with some wood brackets and I have some spackling to do. But it's up and that's all that matters. Now i just have to patch up where the old cadet heater was below.
 