I have a 240V wall heater that I would like to control with an electronic countdown timer
I bought the timer seen in the attached pic thinking it would work since it is rated 120-277V
My electrician so no- it's rated for either 120 or 277V, not from 120 to 277V
I looked around and found another similarly rated countdown timer and contacted their tech support
They said I can use their timer in 120V mode if I "break the neutral"
My knowledge of electrical is pretty limited but what I understood him to say is that I would splice in the timer in one of the two 120V legs that feed the 240V heater
My electrician once again said no- It doesn't work that way
Who's right? Manufacturer or my electrician?
 

Attachments

  • timer.png
    timer.png
    119.8 KB · Views: 7
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,609
Location
Long Island
I've never heard of a device that is rated for 120V or 277V but not 208V and 240V and everything in between, but that doesn't mean it does not exist. Perhaps you can share the model so we can actually look up the specific device you are asking about.
 
OP
1

1190R

Well-known member
Joined
Jul 31, 2014
Messages
252

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
I've never heard of a device that is rated for 120V or 277V but not 208V and 240V and everything in between, but that doesn't mean it does not exist. Perhaps you can share the model so we can actually look up the specific device you are asking about.
looks like it indeed is only rated for 120v and 277v but as you pointed out its not rated for 2000w....
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,941
Location
NJ
I've never heard of a device that is rated for 120V or 277V but not 208V and 240V and everything in between, but that doesn't mean it does not exist. Perhaps you can share the model so we can actually look up the specific device you are asking about.
The switch the OP bought is for lighting circuits. The switch requires a neutral for the load and a grd connection to operate properly.
I'm thinking the neutral and grd have to be at the same potential for the internal circuits to properly work. 208Y/^ & 240 Y/^vac circuits would not have a "neutral load conductor" at the same potential as grd in either of those 4 systems. (240^ corner grounded could be the exception.)