I figured this would be an easy search but I found conflicting information. In any case, what I need is simple, I just wanted a second opinion before I spent the money.
My dad and I are setting a new 125 amp sub-panel for our shop. It is fed from a new main panel located in the same structure. The main panel is 200 amp and the cable run is under 35 feet. They are actually about 15 feet apart but stuff got in the way.
You know how that goes, best laid plans and such . . .
Because of the windy route, we will be using SE Cable rather than pulling the conductors in a rigid conduit, and our plan is to use copper rather than aluminum conductors.
I believe I want to order 2-2-2-4. Does that sound right to the electricians among us?
A second question while I'm at it. There is a portion of this run that I would like to give extra protection. Can SE cable be run through a short length of rigid (+/- 6 feet) or do the same rules apply as for Romex? In other words, not allowed.
Yes this is being inspected. The installation is in Los Angeles County, CA.
Thank you.
My dad and I are setting a new 125 amp sub-panel for our shop. It is fed from a new main panel located in the same structure. The main panel is 200 amp and the cable run is under 35 feet. They are actually about 15 feet apart but stuff got in the way.
You know how that goes, best laid plans and such . . .Because of the windy route, we will be using SE Cable rather than pulling the conductors in a rigid conduit, and our plan is to use copper rather than aluminum conductors.
I believe I want to order 2-2-2-4. Does that sound right to the electricians among us?
A second question while I'm at it. There is a portion of this run that I would like to give extra protection. Can SE cable be run through a short length of rigid (+/- 6 feet) or do the same rules apply as for Romex? In other words, not allowed.
Yes this is being inspected. The installation is in Los Angeles County, CA.
Thank you.