Need help! (ontario canada)
I'm daisychaining(?)12awg wire on a string of receptacles along each wall in my new-construction workshop. I purchased 15ci boxes thinking these were fine, but this is what my box fill calculations come out to:
4 - 4 Conductors in\out of each box except last.
1 - Ground counts as 1
1 - internal clamps count as 1
2 - duplex receptical counts as 2
total of 8 "conductors" = 2.25*8 = 18 cubic inch!
What is the cleanest way to wire several receptacles with 12awg wire?