Can I use 14-2nmb to run about 8 100 watt lt bulbs, I also come accross a roll of 14-3, or should i use 12-2nmb? thanks
 
To avoid these ads, REGISTER NOW!
OP
M

monkers

Well-known member
Joined
Nov 30, 2009
Messages
159
I dont know what you mean about half loaded, 8 100 watt bulbs but I could only use half of them? (im not much of an electrician, sorry for the dumb questions) so if i used 12-2 i could run all 8 bulbs??
 

foolishpride

Well-known member
Joined
Mar 21, 2009
Messages
343
Location
Southwestern Ohio
I dont know what you mean about half loaded, 8 100 watt bulbs but I could only use half of them? (im not much of an electrician, sorry for the dumb questions) so if i used 12-2 i could run all 8 bulbs??

What he meant was having the 8 bulbs will only use about 50% of the allowable maximum load on the #14 wire. By using Ohms Law, those 8 bulbs will draw a little over 6 amps.
 
OP
M

monkers

Well-known member
Joined
Nov 30, 2009
Messages
159
you know, I thought that after I responded.....sorry guys....thank you for the help, where could I find a chart or guide to help me with this stuff, like what size wire for what etc.....or is it way more involved than I should get.....thank you again for the quick replies, tryin to learn a little....
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
14-3 is probably 14-3 w/grd, and you only need 14-2 w/grd.

14-3 w/grd has a white, a red, and a black wire, plus a bare wire for ground.

With incandescent bulbs all you need to do is take the wattage and divide by the voltage (120) to get the amps. Thus each 100 watt bulb draws .83 amps. Lighting loads are continuous and as such you cannot exceed 80% of the circuit rating. So on a 14 gauge wire/15 amp circuit, you are limited to 12 amps........ and on a 12 gauge/20 amp circuit, you are limited to 16 amps.

Not sure why you want to use 100 watt bulbs, thats a lot of current burning up. I'd consider compact fluorescent bulbs (CFL) instead.

Charles
 
Last edited:
OP
M

monkers

Well-known member
Joined
Nov 30, 2009
Messages
159
thank you for the help, Im using 100 watt bulbs becaause the garage is (for now) un-heated, so in the cold weather the fluorescent bulbs usually take some time to start up. Now, I plan on using a Miller trailer furnace (oil, not propane) to warm up the shop while in there, so I will probably put a couple ceiling outlets above the benches, welding area etc to plug in some 4' fl. lts I have that have a string switch to use only the ones I want when I need them. If you see any thing wrong with my plan please tell me ok, thanks for the help guys
 
OP
M

monkers

Well-known member
Joined
Nov 30, 2009
Messages
159
so, fl. lts use less power than reg. bulbs? do they make any for cold weather applications such as mine?
 