Hey Bill,
I'm in Fairview. I used to live in AVL until it really started to get pricey (tax-wise). I know 5000K is daylight and 4500 is very blue/white, but I looked at them in Lowes and you can't stare at them. They'll blind you. They are for a 24 x 28 garage that I'll use for working on my sports cars.
NCtim
Not cans. 4' with two flourescent style strips per unit. Just like T5s but with LEDs and brighter. 4200 Lumens and only 40 Watts per unit. Sorry, I was reading specs off of another box. This is the unit: http://www.ebay.com/itm/181168802444
You may be OK amp/watt wise, but wouldn't you be exceeding the number of allowed fixtures on a circuit?
Huh?
Be careful with lights of america, my experience with there stuff is that it's ****. Don't know about those particular lights but with some othersNot cans. 4' with two flourescent style strips per unit. Just like T5s but with LEDs and brighter. 4200 Lumens and only 40 Watts per unit. Sorry, I was reading specs off of another box. This is the unit: http://www.ebay.com/itm/181168802444
Put in two lighting circuits. The first time you need to replace a fixture after dark you'll thank me.
Sent from my iPhone using Tapatalk
Doesn't the electrical code limit the number of fixtures (receptacles, lights, etc, or a combination thereof) on a circuit to 12 or 14 or something?
OP wanted to put 30 on a circuit.
Find a quote for that...I know up here in Canada there's a 12 device limit per circuit.No limit per nec aside from load limits set by the fixture and figured by ohms law.
Find a quote for that...I know up here in Canada there's a 12 device limit per circuit.
Find a quote for that...I know up here in Canada there's a 12 device limit per circuit.
I was more surprised that the NEC wouldn't list anything because we do have restrictions up here.I said nec not the other code north of the border. BTW the code doesn't tell you what you can do. It tells you what you have to do and what you cannot do. So tell me where it says in the Nec that I can't go higher than 12 devices on a circuit.
I was more surprised that the NEC wouldn't list anything because we do have restrictions up here...
The CEC has a rule about number of outlets or fixtures but the NEC does not....
When it comes to light fixtures, if you know the max rating of the fixture you don't need to use an assumed number like 180VA. If you're installing 6" cans with a max bulb rating of 100W each, you can theoretically install 19 fixtures on a 20 amp circuit at 80% load.
Even if you were only going to use a 50W bulb in the 100W fixture you still have to use the max rating of the fixture because someone could screw in a higher wattage bulb. Now when it comes to LED fixtures I think you can get away with more fixtures if they do not use Edison base bulbs.
The general idea is known load vs. unknown or assumed load. Stuff like this is what differentiates an Electrician from a guy running romex.
So, where do you find 100W incandescent bulbs these days?
The calculations may need some contemporary adjustments.
Be careful with lights of america, my experience with there stuff is that it's ****. Don't know about those particular lights but with some others
100 watt halogen spots could potentially be used.
Power supplies smoked but they weren't these lights.what was your experience? Lots of people have bought them from Sams and seem to have good luck. The ones at Sam's have been rebadged as Honeywell. They have a 5 year warranty.
Be careful with lights of america, my experience with there stuff is that it's ****. Don't know about those particular lights but with some others
Would that include those low voltage outdoor lights that people put along their sidewalks or around a patio or pool?