2-2-2-4 or equivelant copper options

absintheisfun

Well-known member
Joined
Feb 7, 2010
Messages
84
Carrying 70Amps about 50-75 feet, and after seeing not only the price of the 2-2-2-4, but the insane girth, I'm now wondering what my options are...what is the copper equivelant?

And am I going for overkill?

It is going to a sub, and it will be running about 20 110v dual plugs and 2 220v plugs(compressor and later expansion), and 4 lights(dual T12 8')

The girth of the wire kind of threw me because it looks as thick as the copper lines coming into my house!


And then there is the fact that I'm kind of a cheap@ss and am looking for the most cost efficient way to do this....

If the experts here tell me it is the way it is and I need the 2-2-2-4, I'll gladly get it, but would like to explore all possible options.
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
I seriously doubt you have copper coming into your house. I cannot imagine anyone uses copper for service entrance, and you can be sure the power company does not. Part of the size of 2-2-2-4 Mobile home Feeder is the insulation, its pretty thick, since its rated for direct burial.

Charles
 
OP
A

absintheisfun

Well-known member
Joined
Feb 7, 2010
Messages
84
The wires from the meter at least are copper..

As for girth, I am referring to the individual lines...1/4" thick is crazy!
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You'd need #4 copper for about the same capacity as #2 aluminum and also have about 3 to 4 times the money to spend. And if you think 1/4" is crazy you need to see 4/0 aluminum which is commonly used for 200A service entrance. It's over a 1/2".
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I paid $1.46/ft for my 2-2-2-4 at HD. If that's high to you, I'm not sure what to tell you. Copper will easy be three times the cost. 2-2-2-4 is not that hard to work with. Anything in the #4 and up is going to be stiff.
 
OP
A

absintheisfun

Well-known member
Joined
Feb 7, 2010
Messages
84
Yes, I'm cheap. But willing to spend money...just wanted to see what other options were out there.

My Lowes didn't have 2-2-2-4, but they did have 2-2-2(which is how I saw the size) and it was $3.87/ft! I guessed that 2-2-2-4 was going to be almost 5.00/ft.

I figured that copper would be about that much, but maybe a little easier to work with.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
My Lowes didn't have 2-2-2-4, but they did have 2-2-2(which is how I saw the size) and it was $3.87/ft! I guessed that 2-2-2-4 was going to be almost 5.00/ft.
That HAD to be mis-marked. That is WAY more than normal.



I figured that copper would be about that much, but maybe a little easier to work with.
Ummmm.....NO! And yes.
 
To avoid these ads, REGISTER NOW!

offroadsteve

Well-known member
Joined
Apr 28, 2011
Messages
173
Location
Hampton, VA
absintheisfun; said:
My Lowes didn't have 2-2-2-4, but they did have 2-2-2(which is how I saw the size) and it was $3.87/ft! I guessed that 2-2-2-4 was going to be almost 5.00/ft.

I

I bet that price was for 2/0-2/0-2/0, $3.87 a foot sounds about right for that
 

Kevin C

Well-known member
Joined
Aug 4, 2011
Messages
1,653
Location
Portland OR
You'd need #4 copper for about the same capacity as #2 aluminum and also have about 3 to 4 times the money to spend. And if you think 1/4" is crazy you need to see 4/0 aluminum which is commonly used for 200A service entrance. It's over a 1/2".

If the OP can use a 70°C rating, seems to me that #6 copper THHN /THWN an option for 70 amps ( other than the cost).

Is that a fair assumption?
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Using #6 CU THHN he could squeeze out 70A. By the NEC table it is 65A @ 75 deg.C. My comparison was for #2 Al @ 90A, so that's why I said #4 Cu.

If the OP can use a 70°C rating, seems to me that #6 copper THHN /THWN an option for 70 amps ( other than the cost).

Is that a fair assumption?
 

Kevin C

Well-known member
Joined
Aug 4, 2011
Messages
1,653
Location
Portland OR
Using #6 CU THHN he could squeeze out 70A. By the NEC table it is 65A @ 75 deg.C. My comparison was for #2 Al @ 90A, so that's why I said #4 Cu.

Your right, it was 65 amps for 6 gauge, ( again from memory, you are allowed to round up to the next breaker- 70 amps).

Mostly I was bringing it up because I have 6 gauge copper running out to my garage on a 50 amp breaker. If I needed it, I could go up on the breaker size ( assuming there are no voltage drop issues).

Thanks,

Kevin
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Your right, it was 65 amps for 6 gauge, ( again from memory, you are allowed to round up to the next breaker- 70 amps).

Mostly I was bringing it up because I have 6 gauge copper running out to my garage on a 50 amp breaker. If I needed it, I could go up on the breaker size ( assuming there are no voltage drop issues).

Thanks,

Kevin

If the wire is UF-B(direct bury Romex) then its limited to the 60c deg column(55a).
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Yes, I'm cheap. But willing to spend money...just wanted to see what other options were out there.

My Lowes didn't have 2-2-2-4, but they did have 2-2-2(which is how I saw the size) and it was $3.87/ft! I guessed that 2-2-2-4 was going to be almost 5.00/ft.

I figured that copper would be about that much, but maybe a little easier to work with.

You looked at the wrong wire or your Lowes is in high gear rip mode. Last I looked (about 3 months ago) it was $1.89/ft at HD. Our local HD had said they were no longer going to break 500' rolls, but it looks like from the material on the shelf that they are breaking rolls. I bought my wire 18 months ago and the quoted price was $1.79 but when they forklifted the roll down it had a 1.47 sticker on it, so I got it for that. I walked out with 130' of wire, a 20 slot panel with breakers and a 70A breaker for under $250.
 