2-2-2-4 SER application, and installation

woodtn

New member
Joined
Feb 25, 2021
Messages
1
Location
Florida
I'm condensing a few breakers to slim breakers, but same size. I plan on installing a 100a breaker in the main 200a panel in my house, and running wire from it, approx 100ft, to another breaker box in a new shed I bought.

Can I just run 2-2-2-4 SER cable from one roof to another, directly from the 100a breaker, and into the breaker box in my shed?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,794
That application if I understand correctly what you plan on doing would require conduit, and #2 aluminum used in a subpanel can only have a 90A breaker max to use a 100A breaker would require a larger wire size.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You need to run overhead service drop cable that has a messenger support wire and it needs to be installed at the approved height above the ground.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
You would need to use a Quadruplex cable for the outside aerial part. Supported on each end with wedge clamps connected to insulators. You would have to switch over to a different wiring method for the indoor wiring
 