2 car detached garage rewire

dave89iroc

Well-known member
Joined
Mar 25, 2015
Messages
706
Location
outside Detroit, Michigan USA
I'm familiar with some basic wiring, however, I plan on rewiring the garage

2 car detached, it has a single 110v circuit now, a couple switches to lights and 2 outlets, all on 1 swithch in the house


I want to run 220v out there to a small sub panel
220v outlet for future use(60/80 gallon air compressor and maybe a welder, these seem to be rated at ~20A and 30A respectively)
a couple 20A circuits with a couple outlets(probably about 4-5 duplex outlets on each circuit)
2 switched 15A circuits for lights

I plan to dig a trench, and run the plastic conduit, and will be running the individual conductors

the total run is probably right around 50', so, I'm thinking 8 gauge THHN wire?
for that run it looks like it provides for a 50A load ?
so I am looking at a 50A breaker in the house?

or do you recommend a larger wire and corresponding larger breaker?

also, do I run a hot, hot, neutral and a ground, or is a ground rod at the garage called for?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,024
Location
Modesto, CA
I'm familiar with some basic wiring, however, I plan on rewiring the garage

2 car detached, it has a single 110v circuit now, a couple switches to lights and 2 outlets, all on 1 swithch in the house


I want to run 220v out there to a small sub panel
220v outlet for future use(60/80 gallon air compressor and maybe a welder, these seem to be rated at ~20A and 30A respectively)
a couple 20A circuits with a couple outlets(probably about 4-5 duplex outlets on each circuit)
2 switched 15A circuits for lights

I plan to dig a trench, and run the plastic conduit, and will be running the individual conductors

the total run is probably right around 50', so, I'm thinking 8 gauge THHN wire?
for that run it looks like it provides for a 50A load ?
so I am looking at a 50A breaker in the house?

or do you recommend a larger wire and corresponding larger breaker?

also, do I run a hot, hot, neutral and a ground, or is a ground rod at the garage called for?

If u go with #2 AL MHF, u can have 90a, which would be plenty and the wire is probably cheaper than running the #8. #2 MHF is usually around $1.5/ft.

MHF can be direct butied but must be in conduit indoors...

U WILL need 2 ground rods in addition to the 4 conductors(hot, hot, neutral and ground).

The current 120v feed will have to be abandoned.

In the subpanel, make sure to isolate the neutral bar.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The number 2 is great, the 8 too light. If they are close they are often done 6-60 as there is a common cable for it. I agree, if you are piping no reason not to go with a larger wire
 
To avoid these ads, REGISTER NOW!
OP
D

dave89iroc

Well-known member
Joined
Mar 25, 2015
Messages
706
Location
outside Detroit, Michigan USA
The 2-2-4-6 will work okay if you can't find the 2-2-2-4. I don't know where you live, but here the 2-2-2-4 MHF at Lowes (#1.47 a ft) is cheaper than the 2-2-4-6 at Home Depot ($1.69 a ft).

Local Lowes doesnt stock any MHF , home depot does



only 2-2-2-4 at my local lowes is SER, both aluminum and copper


I will look around for the 2-2-2-4 AL MHF though, I like the extra bit of safety
 