I am getting ready to wire my new shop and I want every other plug down the walls to be on separate breakers. Can I use a single conduit down the wall with wires inside form 2 separate breakers?

They do make 600v insulation for communications wire. If you did that, then ok.
Go for it.
I even put two duplex outlets in one 4x4 box.
Each on a seprate breaker.
Two circuits, one box.
We do it in cable tray all the time. Either put a divider between them or insulation rated for 600 volts.
after you have 9 current carrying conductors in one conduit derating progresses to the point where you have to increase wire size. 2 circuits, youre fine.
watch out for those suggesting a MWBC or 2 hots and one neutral if you need GFCI protection. the neutral cannot be shared downstream from a gfci.