2 circuits through one wire?

Boyd Who

Well-known member
Joined
Oct 15, 2007
Messages
1,080
Location
Manitoba
I had a buddy tell me that I could run my garage off 2 breakers on the house panel, but only use one cable out to the actual garage from the panel. Something about a 3-wire run and splitting it in a junction box in the garage.

My plans are to have two 20-amp circuits for the garage. One would power 3 outlets and 3 FL lights, the other would power 3 more outlets and the other 3 FL lights.

I don't need 220 in this garage, but want something better than the current 15 amp service to it. Right now there's only 2 outlets and 4 FL lamps.

Is this possible?
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,685
Location
Maine
I had a buddy tell me that I could run my garage off 2 breakers on the house panel, but only use one cable out to the actual garage from the panel. Something about a 3-wire run and splitting it in a junction box in the garage.

My plans are to have two 20-amp circuits for the garage. One would power 3 outlets and 3 FL lights, the other would power 3 more outlets and the other 3 FL lights.

I don't need 220 in this garage, but want something better than the current 15 amp service to it. Right now there's only 2 outlets and 4 FL lamps.

Is this possible?
Yes this is possible, its called a multiwire branch circuit. Its legal in the US not sure about Canada. You use a 2 pole breaker, hook your 2 hots to the breaker and share a neutral between the 2 hots. You would use a piece of 12/3 nm or pull 1 black, red and white(along with a ground) in a piece of pipe.
 
OP
B

Boyd Who

Well-known member
Joined
Oct 15, 2007
Messages
1,080
Location
Manitoba
Cool, thanks. I'll check with the local electrician on Monday about doing this. I really want to upgrade my little garage before winter.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Is the garage detached? If so, in the USA you cant run more than one circuit without installing a subpanel at the garage. (there are a few exceptions, such as if you have a light on a second circuit which is switched at the house).
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,894
Location
S Cal
If you overload one of your two circuits and the breaker trips - your going to have to walk over to the main panel to reset it?

Sub panels are very cheap - I did a quick search at Lowes.com

783164208306md.jpg


For less then $50, you can buy a small sub panel to install in the garage and run several different circuits. The panel above cost $15

Sub panel is the way to go
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
When I do it, I put the two hots on either side of the panel and the outlets are two duplexs, one for each circuit, in a 4x4 box.
That way have a quick way to just plug into the outlet next to the one you blow and finish the job before going to reset the breakers.
I have always heard them called "Edison circuits."
 

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
The water heater at my old house was wired like that. I guess each breaker controlled one element? Nothing was marked and I was doing some plumbing work. Drained the water heater after turning off 1 breaker (did thing it was odd to have a 120v water heater, but whatever).

Luckily I went back in the house not long after to grab something before running to get parts because the T&P valve had opened up dumping steam out. :shocking:
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
When I do it, I put the two hots on either side of the panel and the outlets are two duplexs, one for each circuit, in a 4x4 box.
That way have a quick way to just plug into the outlet next to the one you blow and finish the job before going to reset the breakers.
I have always heard them called "Edison circuits."

if you are sharing a neutral, you need to use two adjacent breakers, not ones across from eachother, and the breakers need a handle tie.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,685
Location
Maine
if you are sharing a neutral, you need to use two adjacent breakers, not ones across from eachother, and the breakers need a handle tie.

Thats 2008 code, depends if they're on that or not
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Thats 2008 code, depends if they're on that or not

regardless of the handle tie, breakers directly across from eachother will be on the same phase and cannot share a neutral
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Thats 2008 code, depends if they're on that or not

If you don't split the circuit across both buses in the panel, seems to me you will be overloading the neutral when both circuits start to pull some good load. IE - danger condition. And when you want to service one of those outlets or circuit, you want BOTH legs OFF, otherwise you might get an unpleasant surprise.
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,685
Location
Maine
If you don't split the circuit across both buses in the panel, seems to me you will be overloading the neutral when both circuits start to pull some good load. IE - danger condition. And when you want to service one of those outlets or circuit, you want BOTH legs OFF, otherwise you might get an unpleasant surprise.

Yes, the circuit needs to be on both legs but until 2008 code you didn't have to have a handle tie, it could be on 2 single pole breakers. Its up to the person working on the circuit to make sure its off and no danger is present
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
If you will be going to the hassle and expense of trenching and running conduit and wire to your detached,it makes more sense to go to a larger service for only a few dollars more.I wouldn't use anything less than 10/3,8 or 6g would be even better.The subpanel then can be a future option,even if you don't feel you have a need for it now.You will need a two pole breaker,or the handles tied on a wafer type breaker.
 
OP
B

Boyd Who

Well-known member
Joined
Oct 15, 2007
Messages
1,080
Location
Manitoba
Thanks for all the info. Even more confused now than before! lol
I have a subpanel that I can use, but I really don't think it's necessary.
The garage is detached and already has 110V running underground to it off a 15-amp breaker in the house. The most I plan to power out there is my small compressor and Lincoln MigPak 145, plus some lights.
I'll run over and talk to an electrician I know on Monday.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
As MRB noted, in the US you cannot have more than one circuit supplying the detached building. Don't know about Canada. Decent sized feed and the sub panel are the way to go.

Charles
 

hetkind

Banned
Joined
Sep 28, 2008
Messages
995
Location
Johnson City, Tennessee
I would consider that a poor wiring practice, basically you are pulling a single 220v circuit with a center tap. Far better to pull a heavier wire to a sub panel OR run two compeletely seperate circuits. Now you also have to look at the OSHA lockout/tagout standards, 29 CFR 1910.147 and subpart S and see that is would not be allowed in industry.

Right now my shop is being wired with a dedicated 400 amp service to a four hundred amp meter meter socket to two two hundred amp panels.

Howard
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,685
Location
Maine
I would consider that a poor wiring practice, basically you are pulling a single 220v circuit with a center tap. Far better to pull a heavier wire to a sub panel OR run two compeletely seperate circuits. Now you also have to look at the OSHA lockout/tagout standards, 29 CFR 1910.147 and subpart S and see that is would not be allowed in industry.

Yeah right:headscrat, it used in commercial apps all the time. It saves wire , saves current carrying conductors in a pipe and is perfectly legal. Tough to LOTO a 2 pole breaker
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Yes, the circuit needs to be on both legs but until 2008 code you didn't have to have a handle tie, it could be on 2 single pole breakers. Its up to the person working on the circuit to make sure its off and no danger is present

2005 code also required the handle tie if the circuit supplied "more than one device or equipment on the same yoke....." The 2008 code simply makes this requirement mandatory in all multiwire installations, not just most of them.

Its simply good practice

Note that a multiwire circuit cannot be used to supply 240 current. Code says it only can supply line to neutral loads, which equates to 120v loads (you could always disconnect the neutral at both ends and tie it back and use the two hots for a 240 circuit), but you could not use the multiwire circuit to supply both 120v and 240v loads. (you could....., but code doesn't allow it).

Also note that the neutrals have to be wired such that removing a device (such as a defective receptacle for replacement, for example) does not interrupt the neutral.............. Thus all neutrals need to be connected together and then pigtailed to receptacles and other loads.

Charles
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Note that a multiwire circuit cannot be used to supply 240 current. Code says it only can supply line to neutral loads, which equates to 120v loads (you could always disconnect the neutral at both ends and tie it back and use the two hots for a 240 circuit), but you could not use the multiwire circuit to supply both 120v and 240v loads. (you could....., but code doesn't allow it).

Interesting -I wasnt aware of that one.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,685
Location
Maine
2005 code also required the handle tie if the circuit supplied "more than one device or equipment on the same yoke....." The 2008 code simply makes this requirement mandatory in all multiwire installations, not just most of them.

Its simply good practice

I agree its good practice but wasn't code. I use multiwires when the need arises. I'll be using them in my shop and I use them in the field.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I almost always tied the breakers or used a double pole. I use multi wires on occasion especially with long runs where they might get heavier draws.
 