2" Conduit Elbows?

Joel 67

Well-known member
Joined
Apr 26, 2007
Messages
241
I am going to start running the conduit for a 100A sub panel to my garage (My town requires the use of conduit over cable). I will be running #2 THHN in a 2" conduit so that it will be pretty easy to pull.

I went to home depot yesterday to start making a materials list and did not see any 2" EMT elbows. Do they not make them in this big a size or did I just miss them? I could use junction boxes but they cost more than I would think a bent piece of EMT would cost so if elbows are available and would fit then that would be my preference.

thanks!
 
To avoid these ads, REGISTER NOW!

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
The Home Depot in my area (SF Bay Area) has them. 2" EMT 90 degree elbow: $9.08 each. That doesn't sound too bad, but then you have to use two couplings to join each elbow to the straight sections. Those (compression style only; I didn't see the set screw style in that size) cost $39.12 each!!!

$87.32 plus tax per bend!!!

I don't know about you, but that's not OK for me. I have to make a similar run soon, and I plan on using a pipe bender and welded **** joints as opposed to those high dollar parts.
 

Zrexxer

Well-known member
Joined
Jan 23, 2007
Messages
5,058
Location
Pflugerville, TX
I don't know if your code will allow it, but big diameter conduit like that I use the grey PVC conduit instead of EMT. Easy to make nice waterproof joints without expensive fittings as noted above, plus sweeps are readily available. If you have to run EMT check with local electrical supply instead of Home Cheapo, 2" EMT sweeps are available and made in a bunch of different radii.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,000
Location
Minneapolis
Sure, they're available. My guess is Home Depot doesn't carry them (or at least keep them in stock.)

You can also use conduit bodies to make corners, although they may make the pull harder. The most common one is a 'LB' but they come in other configurations, I'm sure you've seen them before.

Here's a picture:
21BUcuoMffL._SS500_.jpg

This one is PVC but you get the idea.
 

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
Also, I'm pretty sure that price applies to each coupling and not to a package of N connectors. Since writing this I have started to second guess myself so I'll confirm it next time I go to HD.

McMaster has the 2" EMT parts. Their 90 degree elbows are about the same price as HD. They have the compression couplings too; $20.94 ea for steel and $8.54 ea for zinc. Also steel set screw style couplings for $14.19 ea. Better than HD, but I'd still rather **** weld the conduit together, using store-bought connectors only where conduit meets J-box. Unless an electrician here gives me a really good reason not to do that.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
not a bright idea to weld.not code either.where did you come up with 89$ per bend?
 

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
Assuming I'm correct in that Home Depot charges $39.12 for each coupler, then two couplers plus one elbow cost $89. That's why I said you would pay $89 per bend if you buy the parts from Home Depot. Like others have mentioned, electrical supply houses might have better prices, plus they would be likely to carry cast zinc or set screw styles that are much cheaper. I only saw steel compression style couplers in the 2" size last time I was at Home Depot.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
just did some work with 2" emt.4$ ea.for screw couplings.10$ each for 90* bend.couplings are steel.this was from ace hardware.i get steel compression for 15.50 ea.cast for 4$.you are getting screwed.
 
Last edited:

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
The price of die cast fittings are thru the roof, generally steel is cheaper
 

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
Not screwed yet; haven't bought anything. I'm here doing my research!

Thanks oleguy, I'll check out ACE. Stock probably varies widely based on location. Home Depot has the highest margin on all the little bits and pieces. That's how I never seem to make it out of there for less than $100.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
since you only need to run three #2 and a #6 for the ground, I would knock it down to 1-1/2in EMT (which allows seven #2, so you will have plenty of extra room to make pulling easy)
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
did not get the 2" comp fittings from ace but an elect supply house.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
but I'd still rather **** weld the conduit together, using store-bought connectors only where conduit meets J-box. Unless an electrician here gives me a really good reason not to do that.

What would you do about possible weld protrusion inside the conduit, which could damage the cable? Aside from the fact that the conduit is UL listed as a system and as such, you have to use the connections intended to be used.

Charles
 

DURAMAT

Well-known member
Joined
Jan 11, 2010
Messages
54
Location
N. Utah
DON'T DO IT! If welding pipe was allowed to
save cost every electrical outfit would be doing it to save $. I don't think it's a accepted means of installation. Plus I doubt your inspector would let it fly. Electrical ain't cheap and there's no way around it, you can't cut corners. Your going to have to pull the prybar out and use it on your wallet :( and I and most prefer the set-screw style over the compression. (unless outside)
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Just find a local electrical supply house.....their prices are typically quite fair....and in many cases cheaper the HD.....
 

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
So I guess I won't be welding, given that new info. If the Home Depot selection and prices were all I had to go on, I would probably still weld. Say what you will about code, inspectors, etc. I'm bootstrapping and I would fix something later if someone forced me to do so.

But now that I know that cheap set screw style connectors are available, I'd go with those. The electrical supply I go to is about 30 miles away and HD is a lot closer, so I hadn't checked there yet. I expect the bulk of the cost with electrical to be in the copper, not the stupid EMT connectors.
 

Keep

Well-known member
Joined
Jan 1, 2009
Messages
1,398
Location
Oshawa, Ontario
How far is the run? How many turns? Does the conduit need to be run the entire length?

I ran #3 copper romex. Most of my run was inside so I only needed to run it in conduit for about 11 feet. I used 1 1/2 emt with one cast 90 at the box and one emt 90 in the run.
 

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
Keep,

Not sure if you were talking to me or the OP, but:

Run will be approximately 40 feet with 3 - 5 bends. All conduit. I haven't worked out the details of it, but I'm definitely trying to keep bends to a minimum. Not just because of cost of couplers, but to make pulling easier. This is for my 3 phase, 50A air compressor. I need to pull three 4 gauge conductors and one 8 gauge (green/ground) through this conduit. Not sure if I should use 1 1/2" or 2" EMT. I want it to be easy to pull.
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Run will be approximately 40 feet with 3 - 5 bends. All conduit. I haven't worked out the details of it, but I'm definitely trying to keep bends to a minimum. Not just because of cost of couplers, but to make pulling easier. This is for my 3 phase, 50A air compressor. I need to pull three 4 gauge conductors and one 8 gauge (green/ground) through this conduit. Not sure if I should use 1 1/2" or 2" EMT. I want it to be easy to pull.

Why are you running such big conduit? How many HP is the compressor? Voltage?
 

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
Why are you running such big conduit? How many HP is the compressor? Voltage?

20 horsepower 3 phase. The motor plate says it draws 50.9A at 220V. I could probably use 6 gauge wire but I have 120/208V service, so, already a tad low on voltage. The 4 gauge wire should have a negligible voltage drop for that current and that length of run. A very experienced air compressor business owner and installer recommended this wire size.

Aceman, what size EMT conduit do you think I should use for three #4's and one #8?
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
4 #4 in a 1".1 1/2 will make it an easy pull.or 1 1/4" which ever you want.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
20 horsepower 3 phase. The motor plate says it draws 50.9A at 220V. I could probably use 6 gauge wire but I have 120/208V service, so, already a tad low on voltage. The 4 gauge wire should have a negligible voltage drop for that current and that length of run. A very experienced air compressor business owner and installer recommended this wire size.

Aceman, what size EMT conduit do you think I should use for three #4's and one #8?

1" is only 32% fill, so it shouldn't be too bad as long as you keep the bends to a minimum or install a pull point in the middle somewhere. HD sells hand benders for 1" emt, if you want to get away from buying factory 90's.
 

cnc-me

Well-known member
Joined
Jan 6, 2010
Messages
1,183
Location
MI
3-4's & 8 will go through 1" conduit Ok.
Just got done running about 30' to my 100A plasma cutter.
Spray some silicone lube into the conduit before you put the sections together.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
3-4's & 8 will go through 1" conduit Ok.
Just got done running about 30' to my 100A plasma cutter.
Spray some silicone lube into the conduit before you put the sections together.

you should only use proper wire pulling lube (cheaper than silicone spray anyways) max for 1in is 4x #4 so yes 3x #4 + 1x #8 is fine
 

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
4 #4 in a 1".1 1/2 will make it an easy pull.or 1 1/4" which ever you want.

1" is only 32% fill, so it shouldn't be too bad as long as you keep the bends to a minimum or install a pull point in the middle somewhere. HD sells hand benders for 1" emt, if you want to get away from buying factory 90's.

3-4's & 8 will go through 1" conduit Ok.
Just got done running about 30' to my 100A plasma cutter.
Spray some silicone lube into the conduit before you put the sections together.

you should only use proper wire pulling lube (cheaper than silicone spray anyways) max for 1in is 4x #4 so yes 3x #4 + 1x #8 is fine

Good to know. Tremendous help. Thanks guys. Helps me because I already have an empty 1" EMT conduit coming out of my panel. I thought I was going to have to tear open the wall and put in bigger EMT.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
in code 358.10. yes if specified for direct bury.corrosion resistant protection judged suitable.
 

cnc-me

Well-known member
Joined
Jan 6, 2010
Messages
1,183
Location
MI
you should only use proper wire pulling lube (cheaper than silicone spray anyways) max for 1in is 4x #4 so yes 3x #4 + 1x #8 is fine

Just usin' what I had around. :bounce:
Doesn't leave any gunk behind, like some wire pullin' lubes.
 

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
I guess the concern with silicone is that it's not compatible with all materials. Maybe it can degrade the wire insulation. I do hate that wire pulling lube though. So messy, can't get it off your hands without washing with soap and water. Makes it hard to handle material.

I'm just writing back on here because I said I'd confirm the Home Depot prices on 2" couplers. They are indeed $39.12 each. It's outrageous.
 

Attachments

  • home depot couplers.jpg
    home depot couplers.jpg
    91.8 KB · Views: 16

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
I guess the concern with silicone is that it's not compatible with all materials. Maybe it can degrade the wire insulation. I do hate that wire pulling lube though. So messy, can't get it off your hands without washing with soap and water. Makes it hard to handle material.

I'm just writing back on here because I said I'd confirm the Home Depot prices on 2" couplers. They are indeed $39.12 each. It's outrageous.

first off emt was mentioned.those are for ridgid conduit not emt.a whole lot of difference.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
I guess the concern with silicone is that it's not compatible with all materials. Maybe it can degrade the wire insulation. I do hate that wire pulling lube though. So messy, can't get it off your hands without washing with soap and water. Makes it hard to handle material.

I'm just writing back on here because I said I'd confirm the Home Depot prices on 2" couplers. They are indeed $39.12 each. It's outrageous.

thsoe are rigid couplings, -compression fittings for rigid are expensive. He is talking about EMT, I just checked and 2in steel set screw couplings are around $5.
 

fusionspecialists

Active member
Joined
Nov 9, 2009
Messages
33
I'm a *******. It being Home Depot, I subconsciously assumed it was like the Rigid brand. I thought the rigid conduit connected with threaded couplings.

Oh well, I learned something.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
just a learning curve.you are not a bumb ***!!rigid can use either threaded couplings or compression.some times you don't have access to threading eq so you use compression couplings.emt or thin wall as it is sometimes called cannot be threaded.
 