2 GFIs in bathroom, one won't reset

Hollywood D

Well-known member
Joined
May 19, 2014
Messages
202
Location
Conifer, CO
I just swapped out two gfi receptacles in a downstairs bathroom. The one next to the sink has both line and load connections. The one next to the toilet has only line connections. The one next to the sink works fine but I'm not getting any power to the one next to the toilet and it will not reset. All other outlets downstream are working correctly.

I have a few questions. Is this second gfi by the toilet even needed since there is already one by the sink? I could swap it to a normal receptacle. I couldn't find anything during a google search that addressed this issue. Or, if I disconnect the gfi by the sink and turn the power back on will it reset the gfi next to the toilet, then reconnect the other gfi that has both line and load?

I have the wires hooked up correctly as well as the ground. I thought maybe the new receptacle was bad so I hooked up the old one and got the same results. Oh and I checked all the other gfi's in the house and none of them are tripped.
 
To avoid these ads, REGISTER NOW!

DirtyJersey

Well-known member
Joined
Sep 13, 2015
Messages
256
Is the breaker on?
Was old receptacle working before you switched it?

Is the receptacle on same circuit as the one by the sink?

Sent from my LG-K550 using Tapatalk
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
Usual cause is mixing up the line and load wires.

The second GFCI might be able to be eliminated ONLY IF it is fed from the load terminals of the first GFCI.
 
OP
H

Hollywood D

Well-known member
Joined
May 19, 2014
Messages
202
Location
Conifer, CO
Breaker is on I checked all of that

Old receptacle was working beforehand, I verified that

As far as I can tell it is on the same circuit as the one by he sink

This house was built in the 80s so I'm sure the original gfis are a retrofit
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,720
Location
Franktown, CO
One GFI shouldn't be fed by another one. Only regular outlets should be fed power from the load terminals of a GFI outlet and they will be GFI protected outlets by default.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
Could be a bad GFCI

Need to test the wires at the toilet GFCI to be sure.

Are you certain that the toilet GFCI is fed from the sink GFCI?
 

DirtyJersey

Well-known member
Joined
Sep 13, 2015
Messages
256
Breaker is on I checked all of that

Old receptacle was working beforehand, I verified that

As far as I can tell it is on the same circuit as the one by he sink

This house was built in the 80s so I'm sure the original gfis are a retrofit
Put feed wires on line side and wire going to receptacle by toilet on load side. Put a regular outlet by toilet.
It will be GFI protected from the one at sink.
Trip the toilet receptacle and gfi at sink should trip if not id recommend calling an electrician.
You can pick up a tester for 10bux that will test gfi circuits.

Sent from my LG-K550 using Tapatalk
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,592
Location
Fullerton, CA
One GFI shouldn't be fed by another one. Only regular outlets should be fed power from the load terminals of a GFI outlet

There is no electrical reason why it shouldn't be done, and both outlets will operate normally
What reason (besides redundancy) do you have against it??
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,421
Location
VT
^^^Same question here.

I know of an entire bar that has GFCI wired line side. Theory is if 1 trips

  • It doesn't kill the whole bar, and service continues
  • The bartender isn't searching for the issue when the blender stops, the outlet RIGHT THERE tripped
 
Last edited:
To avoid these ads, REGISTER NOW!

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
That sounds like they're all wired line side. Not the same thing. Wiring a GFCI to the load side of a different GFCI, it seems to me that either of them could trip during a ground fault.

I know of an entire bar that has GFCI wired load side. Theory is if 1 trips

  • It doesn't kill the whole bar, and service continues
  • The bartender isn't searching for the issue when the blender stops, the outlet RIGHT THERE tripped
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,421
Location
VT
That sounds like they're all wired line side. Not the same thing. Wiring a GFCI to the load side of a different GFCI, it seems to me that either of them could trip during a ground fault.

Yes, I am an idiot, and typed load when I meant line.

I also see how the OP could have wired GFCI #1 line, then GFCI #2 to load side of #1. #1 tripping takes them both out, but #2 tripping only takes #2 out.


Other then a good way to waste $10 on the GFCI I don't see the purpose of having 2 in this case.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Yes, I am an idiot, and typed load when I meant line.

I also see how the OP could have wired GFCI #1 line, then GFCI #2 to load side of #1. #1 tripping takes them both out, but #2 tripping only takes #2 out.


Other then a good way to waste $10 on the GFCI I don't see the purpose of having 2 in this case.

Basically, the results of having a GFCI on the "load" side of another GFCI are undefined if they both have the same trip current. (This could be different if a GFCI breaker and a GFCI outlet was used, since the breaker could have a higher trip imbalance current.)

If there's a fault after receptacle #2, #2 may trip and not #1, #1 may trip and not #2, or both may even trip.

There's not a safety reason not to do so, it's simply usability.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,720
Location
Franktown, CO
There is no electrical reason why it shouldn't be done, and both outlets will operate normally
What reason (besides redundancy) do you have against it??

I've seen nuisance tripping from having them wired in series. I can't explain it, but wiring them parallel (line side only) eliminated it.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,720
Location
Franktown, CO
Of course it isn't literally in series. :rolleyes: I meant series as in the downstream GFIs wired to the upstream load side.
 
OP
H

Hollywood D

Well-known member
Joined
May 19, 2014
Messages
202
Location
Conifer, CO
I wired them up the same way they were originally. Are you saying I should switch the line and load on the one by the sink that's working and see what happens?
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,592
Location
Fullerton, CA
Since you have 2 of them just hook up both to the line connection.

Are you sure you haven't reversed the hot and neutral connection on the recep by the toilet? It's a common mistake and will cause the outlet to not have power.
 