The customer's AC circuit isn't even wired to Code either.
He should have 2 hots and a ground, not 2 hots and a neutral.
He should have 2 hots and a ground, not 2 hots and a neutral.
OP said - "10-3 w/o ground is in use."
I have never seen a "10/3" without a ground, totaling 3 wires.
Not 4 wires as a "Normal" 10/3.
Is there such a thing ever in history ?
Marc
So I’ve been to the house and seen the situation. 10-3 w/o ground is in use. Just wondering as I mentioned above. Can each of those hots share the one neutral. Each hot would be on its own dedicated circuit breaker.
Sent from my iPhone using Garage Journal
OP said - "10-3 w/o ground is in use."
I have never seen a "10/3" without a ground, totaling 3 wires.
Not 4 wires as a "Normal" 10/3.
Is there such a thing ever in history ?
Marc
yes it's a red, black and white. Even stamped right on the jacket it says 10/3 w/o ground.
Over on "ElectricianTalk.com" forum, I just searched for 10/3 w/o ground and there are quite a few references to it. How it was used up into the 80's and early 90's and didn't change until code required 4 wire system.
I guess this was the wrong forum to ask. I thought I'd be treated with respect But I was wrong. I won't be returning to this forum.
Signing off now.

Ignoring the lack of ground, yes two opposite leg circuits (ie 240V apart) can share a neutral. The reason why may not be obvious but here is why. The current has to form a loop too and from the panel, out the hot leg and back through the neutral.* What happens when we add a second leg? The two hots, L1 and L2, always flow in opposite directions. So if L1 is flowing current out, L2 is flowing back to the panel.
Now consider a case where only L1 has a load. Current flows out L1 and back through neutral. If only L2 has a load current flows out neutral and back though L2. If both have the exact same load the current flows out L1 and then back L2. The current flowing through neutral is the difference between L1 and L2.
*Since this is AC voltage the direction is constantly changing but I figure it's easier to think of it as DC and just assume a constant direction.
Interesting. I didn’t know 2 circuits charging a neutral required to be on different legs.