Are octagon boxes REQUIRED for all ceiling boxes ?

Either current or upcoming NEC requires a hot and a neutral in both the switch box and the junction box controlled by the switch. This means 3 wires between the two boxes. Is the black or the red "hot at all times" between these boxes ?
 
To avoid these ads, REGISTER NOW!

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,300
Location
Illinois near St. Louis, Missouri
It shouldn't matter if black or red is hot all the time. Maybe some electricians have a standard way to do it just to keep things straight but as long as its not white or green they are power wires and can be switched or not. NEC doesn't care what color it is as long as its not white or green. At least that's the way I understand it.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,595
Location
Fullerton, CA
Are octagon boxes REQUIRED for all ceiling boxes ?
No. Other boxes qualify. Some fixtures don't require them.

Either current or upcoming NEC requires a hot and a neutral in both the switch box and the junction box controlled by the switch. This means 3 wires between the two boxes. Is the black or the red "hot at all times" between these boxes ?
If you take the wires to the switch box first only 2 wires will be needed.

EDIT: The Code change appeared in the 2014 NEC
 
Last edited:
To avoid these ads, REGISTER NOW!

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
N
If you take the wires to the switch box first only 2 wires will be needed.

EDIT: The Code change appeared in the 2014 NEC

LOL - why putting some wifi control switching in my shop will be a PITA. Have to re-pull nearly every switch leg. Dammit.
 

jeffmattero76

Well-known member
Joined
Mar 26, 2018
Messages
115
Not a sparky, but I think that simply means that the incoming cable goes to the switchbox first, and then to the light fixture. In other words, no switch loops, since there must be a neutral in the switchbox.

Sent from my SM-G530T using Tapatalk
 
OP
T

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,326
Location
SE MI
If you take the wires to the switch box first only 2 wires will be needed.

EDIT: The Code change appeared in the 2014 NEC

Not a sparkie or a "code lawyer" but it was my understanding this was exactly one of the cases they wanted to cover !
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Everyone may have a little different method but I run 2 conductor to all the switch boxes and 3 to the fixtures most of the time. Cap the black hot allows extension, live power or can even be changed for 2 switches.
 