2 wire wifi thermostat?

Rodbolt

Well-known member
Joined
Jan 19, 2013
Messages
67
Location
Grand Junction, CO
So I'm installing my infrared tube heater and I've purchased a Honeywell wifi thermostat model RTH6500WF. What I can't decipher is how to wire it. The heater diagram shows two wires, one is 24 volts AC and the other is signal to turn on heat. The thermostat does not show any instructions for a two wire setup but does require a 24 volt common to the C terminal. Can I simply run 24 volts to C and hook the signal wire to the W terminal? I'm hoping someone out there has gone down this road before. I've included a link to the Honeywell instructions and an image of the heaters wiring schematic. Thanks for your help!

http://www.wifithermostat.com/Resources/Pdf/RTH6580WF-User-Guide-English-French.pdf


Sent from my iPad using Tapatalk HD
 

Attachments

  • ImageUploadedByTapatalk HD1387684571.986130.jpg
    ImageUploadedByTapatalk HD1387684571.986130.jpg
    135.7 KB · Views: 55
To avoid these ads, REGISTER NOW!

mooseeater19

Active member
Joined
Nov 29, 2013
Messages
31
Location
BC Canada
The stat in the wiring diagram does not have a (c) common.
The wifi stat requires a (c) common

24volt transformers have a 24vac(r) and common (c) terminals.
The switch leg out of a thermostat is on the (w) terminal.
You need a 3 wire to the stat.
 

rtcblc

Member
Joined
Jul 9, 2013
Messages
14
I installed this same thermostat and had to use one of the alternate wiring schemes. But not a 2 wire system. I'd just call there 800 number for tech help. Might be the easiest way to find out a correct answer. BTW-I'm pleased with the thermostat have had it for about 4 months and when it was -20 below recently it was reassuring to check on house temp from 350 miles away.
 
OP
R

Rodbolt

Well-known member
Joined
Jan 19, 2013
Messages
67
Location
Grand Junction, CO
The stat in the wiring diagram does not have a (c) common.
The wifi stat requires a (c) common

24volt transformers have a 24vac(r) and common (c) terminals.
The switch leg out of a thermostat is on the (w) terminal.
You need a 3 wire to the stat.

So is the common (c) terminal essentially ground? I looked at the transformer in my heater and one output wire goes to the 24 volt pin on the control module and the other output wire goes to a chassis ground. I have plenty of wires in the wall. Can I hook my "C" wire to that chassis ground and make this thing work?


Sent from my iPad using Tapatalk HD
 

mooseeater19

Active member
Joined
Nov 29, 2013
Messages
31
Location
BC Canada
So is the common (c) terminal essentially ground? I looked at the transformer in my heater and one output wire goes to the 24 volt pin on the control module and the other output wire goes to a chassis ground. I have plenty of wires in the wall. Can I hook my "C" wire to that chassis ground and make this thing work?


Sent from my iPad using Tapatalk HD

Short answer , yes
I had a hard time seeing the wire diagram clearly so I wasn't quite sure where the common side of the transformer was going.
:thumbup:
 
OP
R

Rodbolt

Well-known member
Joined
Jan 19, 2013
Messages
67
Location
Grand Junction, CO
Sorry for the hard to read diagram, here's the link. It's toward the very end of the document.

Mooseeater, the diagram does not show where the common goes, I figured that out by studying the heater itself. It sounds like running the C wire to the chassis ground should make this baby fly. Hopefully I can let you know later today!


Sent from my iPad using Tapatalk HD
 

Rockhead261

Well-known member
Joined
Aug 28, 2013
Messages
1,911
Location
10509
So is the common (c) terminal essentially ground? I looked at the transformer in my heater and one output wire goes to the 24 volt pin on the control module and the other output wire goes to a chassis ground. I have plenty of wires in the wall. Can I hook my "C" wire to that chassis ground and make this thing work?


Sent from my iPad using Tapatalk HD

HVAC guy checking in.

It'll work long enough to make you feel good about it, but it will fail soon thereafter. C is not a ground. It's the common side of the transformer.

Don't ground the C terminal. This is not the old days where the thermostat was comprised of a mercury switch that would tolerate dirty voltage. You are dealing with sensitive electronics. You risk cooking your stat, the transformer, the system control board, or all three. Do it correctly and run a 3 wire.

Sent from my SCH-I545 using Tapatalk
 
Last edited:
To avoid these ads, REGISTER NOW!

mooseeater19

Active member
Joined
Nov 29, 2013
Messages
31
Location
BC Canada
Sorry for the hard to read diagram, here's the link. It's toward the very end of the document.

Mooseeater, the diagram does not show where the common goes, I figured that out by studying the heater itself. It sounds like running the C wire to the chassis ground should make this baby fly. Hopefully I can let you know later today!


Sent from my iPad using Tapatalk HD

You want it connected to the c side of the transformer. when you say chassis ground if you mean where the wire from the common side of the transformer connects to the chassis , I think that is fine.
It's common to ground the c side of a transformer grounded .
 

Rockhead261

Well-known member
Joined
Aug 28, 2013
Messages
1,911
Location
10509
You want it connected to the c side of the transformer.

Correct.

when you say chassis ground if you mean where the wire from the common side of the transformer connects to the chassis , I think that is fine.
It's common to ground the c side of a transformer grounded .

Be careful. Just because the common side of the transformer might be grounded, I'll betcha a paycheck it's also wired directly to relays and boards and anything else that might require the common side of the transformer.

Don't use an earth ground as a conduit for a common. The thermostat requires C. Wire it to C.
 

mooseeater19

Active member
Joined
Nov 29, 2013
Messages
31
Location
BC Canada

tgb

Well-known member
Joined
Dec 16, 2012
Messages
121
Location
Southeast Iowa
You'll also need to get into the setup on the t-stat and set it up for like a boiler or gravity heat or it will not work like it should because it will cycle too short. In all reality you should use a line voltage stat or a cheap bimetal stat with radiant for these type of systems or the flue pipe and tubes will start to rust out because they won't run long enough on a digital stat.
 
OP
R

Rodbolt

Well-known member
Joined
Jan 19, 2013
Messages
67
Location
Grand Junction, CO
HVAC guy checking in.

It'll work long enough to make you feel good about it, but it will fail soon thereafter. C is not a ground. It's the common side of the transformer.

Don't ground the C terminal. This is not the old days where the thermostat was comprised of a mercury switch that would tolerate dirty voltage. You are dealing with sensitive electronics. You risk cooking your stat, the transformer, the system control board, or all three. Do it correctly and run a 3 wire.

Sent from my SCH-I545 using Tapatalk

Ok, let me clarify. The common side of the transformer goes to a stud on the inside of the metal box along with some other wires. I intended to run my third C wire to that stud. I'm not going directly to earth ground unless it is connected to the metal box also. I'm assuming that the C wire is simply needed to complete the 24 vac circuit to run the thermostat controls when the heater is off.


Sent from my iPad using Tapatalk HD
 
OP
R

Rodbolt

Well-known member
Joined
Jan 19, 2013
Messages
67
Location
Grand Junction, CO
Thanks for all your help guys! She's wired up and running!