I read them last night.
Fully explaining my concerns and reasons would bring on a discussion that would violate forum rules. That said, if the two compressors are going, it is a hot day, the 3-ton AC is going, all the LED lights in the garage are lit up, a couple loads of laundry are being done, the refrige is cooling, and the other half gets out of the shower then flips on the hair dryer ... .
As to load calcs, this is what i had to put together when installing the surge protector. The only difference is that now the AC is 3-ton.
220.12 General Lighting Load
1343 sqft x 3 va per sqft = 4,029 va
220.52(A) Small Appliance Load 1500 va per each 20 amp in kitchen, table area, etc. Specific circuits used already include microwave and refrigerator 2 ea at 1500 va = 3,000 va
220.52(B) Laundry Load 1 x 1500 va = 1,500 va
________
Total General Lighting & Appliance Load = 8,529 va
220.42 Lighting Load Feeder Demand Factor
1st 3000 or less at 100% = 3,000 va
3001 to 120,000 at 35% (5,529 x .35) = 1,935 va
__________
Total Lighting & Small appliance load 4,935 va
220.54 Electric Clothes Dryers
Total 1 (sticker indicates 3,300 va) 5,000 va
220.55 Electric Cooking-Ranges, Stove tops and wall ovens
-0- (house has gas stove, gas water heater and gas furnace)
220.51 Fixed Electric AC (gas heating)
2.5 ton
[15 RLA + (.50 FLA x 125%) =15.625 X 230VAC = 3,593 va
HVAC blower motor 876 va
________
Total HVAC 4,469 va
220.14 Wired Appliance Load
Dishwasher 1,200 va
Range Hood 240 va
Bath room Vent fans 2 ea at 100 va each 200 va
Hanging fan 90 va
Whole House Fan 850 va
__________
Total Wired Appliance Load 2,580 va
220.53 Motor Loads
½ hp Garage door opener 375 va
½ hp Garbage disposal 375 va
2 ea Craftsman air comp. (tag 2ea X 7.5A x 220V) 3,300 va (these are non-continuous and are not often used)
__________
Motor load 4,050 va
Total Whole House Load 21,034 va / 240V = 87.64 amps
GE 125amp panel x 240V = 30,000 va X .80 = 24,000 – 21,034 va load = 2,966 va panel surplus / 240v = 12.36 amp surplus at 80%
Power Company Service has a 13.4% surplus = 3,216 va / 240V = 13.40 amp surplus