If the shut off breaker(some breaker just after the meter) is 200 amps would code allow wiring a 100 amp sub panel and a 200 amp main panel?
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
You could add a sub-panel off the main panel. You CANNOT simply tap of the bottom of the 200A main breaker. You must have a sub-feed breaker in it's own spot.
 
To avoid these ads, REGISTER NOW!

bill in in

Member
Joined
Feb 15, 2014
Messages
17
Check the branch breaker space ampacity, most would be good for 100A. You could change out the panel to a pass through type and then connect to the second lugs, or install a disconnecting device (probably fusible) ahead of the original panel and feed all off of it (see the specific sections - this isn't as good an option as it would seem).

You might want to check your service. If you haven't got the ampacity coming from the power company, why waste you money? Don't pay for service larger than you need or have capacity for.
 