Here's the plan:
1-Set two poles, one mid span on their existing line other side of the road and the other along roadside on our property
2-Run primary underground cable to a transformer 320' off the road. Cable length will be longer due to route it takes and going up pole.
3-Set 25kv transformer on ground vault
4-Run secondary line to nearby 200A meter then outdoor 200A feedthrough panel with room for 8 additional circuits. from there to house once built.
All this for around $6900, but wait there's more.....
Power company supplies and install two poles, overhead wires to cross street, and 25kv transformer, makes all connections.
Power company does NOT supply or install trench, primary underground cable, conduit, transformer base, meter pedestal, meter cabinet, or outdoor feedthrough panel. Everything beyond the meter is all our responsibility, which is normal. That's right folks all that is on top of the $6900, plus I have to install it all. I knew that there was going to be a hefty bill to get this done right. I was surprised when the line engineer said they don't run the underground cable, only make the connections.
I was able to find a supply house for the primary URD, 15KV #2AL 220 insulation full concentric neutral. $2100
Fiberglass transformer base - $500
Conduit - $1000
Meter can, outdoor panel, misc. - $700
Excavator for one day - $500
Total Approx - $12000