Looking at putting a 200 amp service in my shop. I have a 325 amp meter socket with a double lug set up at the house so looking to pull from there, the distance is 400 feet to shop. What size conduit and wire should I be using and is a 200 amp service really necessary, using the standard air compressor, 220 welder, etc.

Thanks.

Edit: I am not an electrician so I may be way off base with this.
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

Pwrgeek

Well-known member
Joined
Oct 18, 2015
Messages
288
Location
Texas USA
400' is a long run. You're going to be looking at some large wire to keep the voltage drop manageable.

At 400' the minimum you'd need is 350MCM Cu or 500MCM Al. You could get away with a smaller neutral if the legs are well balanced at the shop but it's still going to cost a pretty penny.


Sent from my iPhone using Tapatalk
 

bdk1976

Banned
Joined
Feb 19, 2007
Messages
285
Is reevaluate your needs- seriously doubt you need 200a if this is a home (and/or) one man shop.