mx842
Well-known member
I'm building a post frame, medal siding pole barn/shop behind my house. When I built my house I knew that one day I would build a building out back so I had 400 Amp service installed at the time. This means I have two 200 amp service panels side by side that one was supposed to be for the house and the other was supposed to be left empty for the proposed outside building.
As luck would have it the electrician put half the house in one box and half in the other and it was all buttoned up by the time I saw what he had done so I just left it as it was until now I need the juice for the building.
I spent most of the day yesterday moving circuits out of one box and running them into the house panel box. I left a few circuits in the box that will go to the garage like the receptacles and ceiling lights in the attached garage, my well pump and some outside lights and moved the rest to the other box.
This freed up the second panel for the use to my shop. The shop is around 200 feet from the main breaker panel and I am using a 4 wire Aluminum service cable that is, 4/0 -4/0- 2/0- 4. This is going into 21/2" conduit and will be buried out to the new building. The problem I find myself in now is how do I connect this big azz wire to my 200 Amp panel at the house? I thought about drilling and tapping the buss bar then adding studs for terminal connections but I'm not sure if this is a good idea or not.
I know I could get an outside 200Amp disconnect and go in through the meter base box but that would mean I would have to have the power company come out and pull the meter so I could connect there but that would probably require some kind of permit and inspection from the county and I don't want to open up that can of worms.
I have heard of people talking about some kind of connection kit you can buy to connect into the main service panel to go out to a sub but I can't find anything out about these for 200 Amp service. All I can find is 100Amp breakers that will fit into my box.
As luck would have it the electrician put half the house in one box and half in the other and it was all buttoned up by the time I saw what he had done so I just left it as it was until now I need the juice for the building.
I spent most of the day yesterday moving circuits out of one box and running them into the house panel box. I left a few circuits in the box that will go to the garage like the receptacles and ceiling lights in the attached garage, my well pump and some outside lights and moved the rest to the other box.
This freed up the second panel for the use to my shop. The shop is around 200 feet from the main breaker panel and I am using a 4 wire Aluminum service cable that is, 4/0 -4/0- 2/0- 4. This is going into 21/2" conduit and will be buried out to the new building. The problem I find myself in now is how do I connect this big azz wire to my 200 Amp panel at the house? I thought about drilling and tapping the buss bar then adding studs for terminal connections but I'm not sure if this is a good idea or not.
I know I could get an outside 200Amp disconnect and go in through the meter base box but that would mean I would have to have the power company come out and pull the meter so I could connect there but that would probably require some kind of permit and inspection from the county and I don't want to open up that can of worms.
I have heard of people talking about some kind of connection kit you can buy to connect into the main service panel to go out to a sub but I can't find anything out about these for 200 Amp service. All I can find is 100Amp breakers that will fit into my box.