I'm looking for some advice from someone who may have a similar panel configuration or installed service like this before.
I recently had our service upgraded to 200A by my provider. I was told they would install a new meter panel with slots for up to three breakers. This was after I explained my intention of splitting the service with 100A to the house and 100A to the shop.
What I got was a 200A meter panel with one new 200A breaker which I paid them $150 for. I was not available to check the install so I did not discover this until after the crew was done and gone for the day.
After several discussions with the provider (asking if they could swap out the meter panel with the configuration I was looking for) I was told "whatever is past the meter is your responsibility" Ok, I'll have to make this work somehow.
I've had three electricians on-site and they have given me different options ranging from installing a new sub-panel on the back of the pole with two, 100A breakers or installing a new sub-panel on the back of the house with a 100A breaker for the shop.
This is the current setup in the two buildings:
Main panel in the house has two 90A breakers feeding out to the shop with direct burial. All conductors are 4 ga. aluminum (120V / 120V / Neutral) Ground rod installed near the shop panel. I know that's not up to code as one electrician looked at it said, "that's how they used to do it." Maybe back in the late 70s and early 80s I guess? The shop has an old GTE / Sylvania panel with Zinsco, Z-style breakers.
That's going away to be replaced with a new panel with this project.
View from shop up to the house:
Overhead feed to from meter to the house panel and conduit feed to underground out to the shop
In my last call with the electric provider they recommended I call the electricians back out again because I do not need a sub-panel on the pole; they could just use the two open lugs coming off the 200A breaker:
New 200A meter panel
That's where the confusion and my question comes in. Do I really need to have a sub-panel on the pole to split out the service? The new panel in the shop will have a 100A main breaker on it. I have a quote for close to $4,000 to have everything installed:
I recently had our service upgraded to 200A by my provider. I was told they would install a new meter panel with slots for up to three breakers. This was after I explained my intention of splitting the service with 100A to the house and 100A to the shop.
What I got was a 200A meter panel with one new 200A breaker which I paid them $150 for. I was not available to check the install so I did not discover this until after the crew was done and gone for the day.
After several discussions with the provider (asking if they could swap out the meter panel with the configuration I was looking for) I was told "whatever is past the meter is your responsibility" Ok, I'll have to make this work somehow.
I've had three electricians on-site and they have given me different options ranging from installing a new sub-panel on the back of the pole with two, 100A breakers or installing a new sub-panel on the back of the house with a 100A breaker for the shop.
This is the current setup in the two buildings:
Main panel in the house has two 90A breakers feeding out to the shop with direct burial. All conductors are 4 ga. aluminum (120V / 120V / Neutral) Ground rod installed near the shop panel. I know that's not up to code as one electrician looked at it said, "that's how they used to do it." Maybe back in the late 70s and early 80s I guess? The shop has an old GTE / Sylvania panel with Zinsco, Z-style breakers.
That's going away to be replaced with a new panel with this project.View from shop up to the house:
Overhead feed to from meter to the house panel and conduit feed to underground out to the shop
In my last call with the electric provider they recommended I call the electricians back out again because I do not need a sub-panel on the pole; they could just use the two open lugs coming off the 200A breaker:
New 200A meter panel
That's where the confusion and my question comes in. Do I really need to have a sub-panel on the pole to split out the service? The new panel in the shop will have a 100A main breaker on it. I have a quote for close to $4,000 to have everything installed:
- New subpanel on the pole with the overhead lines for the house re-routed over to it
- Two 100A breakers (one for house, one for the shop)
- Underground metal conduit from new subpanel out to the shop with new wire
- New panel installed in the shop