200amp service at a long distance

DaveInTX

Active member
Joined
May 29, 2020
Messages
37
Location
Texas
I'm just thinking out loud here, so bear with me... So a new 200amp service requires 2/0 copper or 4/0 aluminum - but if this 200amp service is about 150' away from the PoCo meter, I would probably need to upgrade to 3/0 copper to account for voltage drop, right?

Only issue with this I've seen, is most of the 200amp panels, at least the GE ones that I'm familiar with (the brand that was installed on our house) only handle up to 2/0 wire at the lugs. Are there are adapters to step-down from a 3/0 wire to a 2/0 lug? Is this allowed? Or would I need to source a panel larger than 200amp to accommodate the 3/0 wire? Thoughts?
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
Are you sure that isn't the minimum size of the lug?
All panel's (and breaker's) lugs accomodate the maximum expected wire sizes
 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
Square D 200 amp mains can take up to 250 mcm, I'm sure other brands are the same. 150' is nothing to be concerned about for a 200 amp service. Mine's about that far and I didn't give voltage drop a second thought.

The current GE catalog shows all 200 amp main breakers accepting at least a 250 and a couple that will take a 300.
 
Last edited:
OP
D

DaveInTX

Active member
Joined
May 29, 2020
Messages
37
Location
Texas
Thanks all! I must've been misreading the GE tech specs - looking at them now, I can see that the GE specs do say 250 mcm - not sure where I was reading the 2/0...

That is good to hear that the general consensus is that voltage drop isn't a huge concern at that distance. Ideally I'd be able to run 2/0 cable to avoid the price increase at 3/0.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
Thanks all! I must've been misreading the GE tech specs - looking at them now, I can see that the GE specs do say 250 mcm - not sure where I was reading the 2/0...

That is good to hear that the general consensus is that voltage drop isn't a huge concern at that distance. Ideally I'd be able to run 2/0 cable to avoid the price increase at 3/0.
Why not use 4/0 aluminum?
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,505
Location
SE MI
Is this for a garage/shop ? I can not imagine the need for 200A service unless you are planning on inviting a bunch of buddies over for a welding party. Just because the panel says it is 200A does not mean you need to FEED it with 200A. Worst case would be tripping the breaker that feeds the wire.

A one man operation can get buy with 100A. Even 60A will run a welder and a mini-split. You might have to turn off the A/C if you are using a plasma cutter.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Have you priced out that 2/0 copper and compared it to 4/0 aluminum? Copper will be about double. If you have a disconnect at the meter, that means a 4 wire feed.

That's a huge amount of extra spend for no gain other than slightly smaller wire
 

mcbane

Well-known member
Joined
Jul 23, 2017
Messages
794
Location
California
200 amps, 150' run, 4/0 aluminum is only 2.7% voltage drop for a 240 volt circuit. And even if you one of the GJ people with 220 volt power, would be only 3% voltage drop.

And as a practical matter, feeders are almost never running at full current so typical voltage drops would be far less. If you want to avoid voltage drops at sensitive tools your money is better spent selectively upsizing longer branch circuit conductors.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,630
Location
BC
I'd run 250kcmil alum if you anticipate max capacity out there. Fits in any 200A residential panel lugs in my experience.

Would be direct-burial cable for me. If doing conduit, consider the length of the run and probably needs to be oversized to pull in easy.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,786
The OP has not specified what the service is for, & 4/0 AL, or 2/0 CU, is for dwelling services, for other applications if the load is 180A or less then the next standard size up of fuse or circuit breaker can be used.
 
OP
D

DaveInTX

Active member
Joined
May 29, 2020
Messages
37
Location
Texas
Thanks all for the comments! My first post was (intentionally) a bit vague - maybe I can shed a bit more light. I'm putting in a new shop about 100' from my house, and exploring what my options are for getting power to it.

Currently, my electric meter (200 amp service) is installed on my house - it's fed by an aerial cable from a pole-mounted transformer ~125' away. From what I can tell, I have two options to get power to the shop (shown in the picture).

Option A - run new cable (underground, thinking MHF) from my existing house-mounted breaker panel to the shop. I think 100 amp would be more than adequate. Problem is, the breaker panel and subpanel next to it are already very full. I could potentially replace the subpanel with a larger one, and then run my new 100amp wire from there.

Option B - move my electric meter back to the utility pole - my PoCo doesn't have any issue with this. From there, I'd run 200 amp service (underground) to the shop, and then feed-through 200 amp service (underground) to the house. In this scenario, the intent with feeding from the shop to the house (rather than from the house to the shop) is so that I can install a generator + transfer switch at the shop, and then power the house in the event of an outage. I'm thinking this would involve running 4/0 aluminum (or 2/0 copper) from the pole -> shop -> house. I'd also have to split the grounds and neutrals in the house panel, since it'd be converted a subpanel.

Option A seems more realistic - the main downsides being 1) have to figure out some way to fit the 100amp wires in the existing breaker panel, 2) I can't feed the house from a generator located at the shop (not a deal-breaker), and 3) we were going to use this as an excuse to take our aerial cable underground (which Option B would've done).

Option B seems more expensive (especially if I have to use copper), and problematic if I can't fit 4/0 aluminum in the lugs of my current panel.

Some might say "add another electric meter to the shop, and just run a new leg from the pole to the shop" - I'm trying to avoid this, as the PoCo charges per meter per month.

This may seem confusing given my original post - in my head, my original post was based on the idea of using 2/0 copper for "Option B", under the assumption that 4/0 (aluminum) wire doesn't fit in my existing breaker panel.

Now that you know the "full" story, I'm very curious to your opinions on this. Thanks!
 

Attachments

  • Presentation1.jpg
    Presentation1.jpg
    66 KB · Views: 21

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
You could do a and run a feed from the generator back to the transfer switch at the house. It's extra wire, but doable

You can't install a couple tandems to free up two spaces for the breaker to feed the shop?
 
OP
D

DaveInTX

Active member
Joined
May 29, 2020
Messages
37
Location
Texas
You could do a and run a feed from the generator back to the transfer switch at the house. It's extra wire, but doable

You can't install a couple tandems to free up two spaces for the breaker to feed the shop?
Thanks Mike! You know, I didn't think about that (running a second line)... I'll dig into it and see if it makes sense with my application.

And my panel is already pretty full of tandem and 1/2" breakers, so there's not much room to spare. There are a couple full-size breakers left, but those are feeding other subpanels around the house.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,964
90a is far cheaper to put in than 100a.

if you have 2 240v circuits use a quad and free up space for the 90/etc garage feed.

1657682666687.png
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Thanks Mike! You know, I didn't think about that (running a second line)... I'll dig into it and see if it makes sense with my application.

And my panel is already pretty full of tandem and 1/2" breakers, so there's not much room to spare. There are a couple full-size breakers left, but those are feeding other subpanels around the house.
Subs can be fed from tandems, just need a handle-tied quad like @jeepxj is showing.

Although it may be a good opportunity to think about some rework if things are getting messy from the complexity
 
OP
D

DaveInTX

Active member
Joined
May 29, 2020
Messages
37
Location
Texas
Thanks for the responses all!


Subs can be fed from tandems, just need a handle-tied quad like @jeepxj is showing.

Although it may be a good opportunity to think about some rework if things are getting messy from the complexity

Your comment there is kind of why I'm leaning towards "Option B" (i.e. moving the meter back to the utility pole and running new wire from the pole -> shop -> house). It will be a bit more $$ up front, but I could definitely use some space in my breaker panel, and it'll give me the option of feeding the house from a shop-located generator.

With the all-in price-per-foot, it (surprisingly) almost makes sense to run separate 2/0-2/0-2/0-4 copper THHN/THWN-2 wires, versus 4/0-4/0-4/0-2/0 Aluminum MHF.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
With the all-in price-per-foot, it (surprisingly) almost makes sense to run separate 2/0-2/0-2/0-4 copper THHN/THWN-2 wires, versus 4/0-4/0-4/0-2/0 Aluminum MHF.
Huh? 2/0 copper is about $4-5 a foot, each. The entire 4/0 MHF is $10. Plus the THWN requires conduit, while the mhf doesn't .

If you are running conduit, use aluminum xhhw. Your four conductors will be under $9 a foot, total.

It's your money, but mine would be buying aluminum at that size
 
OP
D

DaveInTX

Active member
Joined
May 29, 2020
Messages
37
Location
Texas
Valid point, and I appreciate the insight. I was planning on running conduit, regardless of using aluminum or copper wiring. If I run the copper (2/0), it looks like I can get by with 1.5" conduit; if I go with aluminum (4/0), I'll have to bump up to 2" conduit (per the Southwire conduit fill calculator - I'm open to recommendations though if anyone has any). It's not a huge deal, but 1.5" will probably save me $8 or so per 10' stick.

I've found 2/0 THHN/THWN-2 locally for $2.84/ft - that's why I was leaning towards copper. For the four wires, it's right around $10/ft. But I didn't think about the aluminum XHHW, so that is another option on the table...
 

rharman

Well-known member
Joined
Apr 22, 2012
Messages
9,029
Location
SoCal
90a is far cheaper to put in than 100a.

if you have 2 240v circuits use a quad and free up space for the 90/etc garage feed.

1657682666687.png

Not to hijack the OP's thread but curious....

Is the quad two independent 240V breakers? Meaning that the inner & outer handle pairs are NOT tied to each other?
I have this in my panel and I assume it's for our pair of A/C compressors (label is really faded).

Thanks!
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,192
Location
Modesto, CA
Not to hijack the OP's thread but curious....

Is the quad two independent 240V breakers? Meaning that the inner & outer handle pairs are NOT tied to each other?
I have this in my panel and I assume it's for our pair of A/C compressors (label is really faded).

Thanks!
yes
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Valid point, and I appreciate the insight. I was planning on running conduit, regardless of using aluminum or copper wiring. If I run the copper (2/0), it looks like I can get by with 1.5" conduit; if I go with aluminum (4/0), I'll have to bump up to 2" conduit (per the Southwire conduit fill calculator - I'm open to recommendations though if anyone has any). It's not a huge deal, but 1.5" will probably save me $8 or so per 10' stick.

I've found 2/0 THHN/THWN-2 locally for $2.84/ft - that's why I was leaning towards copper. For the four wires, it's right around $10/ft. But I didn't think about the aluminum XHHW, so that is another option on the table...
That's a good deal for 2/0 copper. Yeah, check them for the AL and if it isn't materially cheaper, copper is the smart play.
.that is going to be a hell of a pull through 1.5". The entire time, you will be wondering why you didn't spend the extra couple hundred for 2"...


Do 2". Use lots of lube and get two friends to help.
 